hi, i was wondering as i calculate the cable size of a run of swa do i use the total ampage or the line ampage? for example my run is 95 meters and total current is 273 amp. the cable is spaced in horizontal cable tray.
Hello, I really need to know if it's possible to calculate the power factor from the voltage and the wattage...
For example...
13kW, 400 V three-phase machine
Thank you
Good evening all,
I just joined the community and I really hope I can contribute as much as I could be helped. Really.
I'm completing my 2365 lvl3 course however I just got my 305 B assessment paper back. Apparently I didn't calculate well the max. Demand and diversity of a given circuit...
a local pub i do alot of work for wants to build 6 pod style holiday lets in its beer garden and has applied to western power to see if the existing supply can cope with the demand
the existing supply is 2 phase with a 200 amp fuse in each phase leading to a busbar system. ive been asked to...
Hi guys,
Am I doing Continuity test calculations in a right way?
For unknown length of a cable:
Circuit breaker B16A, let Ze be 0.26 ohms. Zs from Table B6 (OSG, p125).
MAX Zs-Ze = Max expected (R1 + R2) = 2.2 - 0.26 = 1.94 ohms
For known length:
Let's assume the cable is twin with 1.5x1.5mm2...
Hello Gents
Once again I’m looking for your expertise to resolve the following application.
A local supply Authority has supplied a single phase 8Kw TN-C-S supply via a cut out, to which we have to terminate a 35mm2 3 core SWA cable to be buried underground. The cable cannot be easily...
Dear All,
I have a problem. It's calculating inverter for 3 pharse non-synchronous. I mean that i don't know the formula. My colleagues show
Here we go :
P1/P2 = (n1/n2)3
Please help me out
Thanks
Good evening!!
i have recently been looking into earth electrode systems, which got me onto reading BS 7430:2011. I am hoping that someone on here can clear a few things up for me.
First of all, is there a reason why BS 7430:2011 makes no reference at all to non homogeneous soil types? It...
Hi guys,
After sitting down and working out all my fixed and variable overheads I have worked out charging a maximum hourly rate of £28-30 per hour working 220 days of the year.
If I only worked 150 days of the year, as this is my first year trading, I will need to charge £33 per hour.
I have...
Feed in Tariff and Export Tariff payments are Tax free. When calculating pay back does anyone take this into account? The payment is effectively what would have been received after tax was deducted had it been taxable. For a 20% tax payer, it means the payment is actually worth 25% more. For the...
I have a question.I have seen plenty of people ask here how much they should charge for certain things in their business. I have also seen plenty of men ask here ask various other questions about starting out and other related questions.
I would like to know how many of you would find a book or...
Is it possible to calculate Ze?
I am in the middle of an assignment, and have this question to answer.
When confirming automatic disconnection of the supply it is necessary to determine the external earth fault loop impedance(Ze) of the system. State three methods by which this can be...
I need to calculate the Zs for a ring main that uses the metal conduit as CPC. I know that Zs = Ze + R1R2 but I only have an R2 reading as there is no wired CPC. Anyone got a clue?
I have been looking at this today and found it interesting so thought i would post a question for any of you to answer.
Calculate the neutral current on a lv 3 phase system.
L1 = 30Amps
L2 = 60Amps
L3 = 22Amps.
I understand that the formula to work out a 3 phase current is
I= P/(1.732 * V * pf)
I have a 3 PH+N water pump rated at 4kw, so
I= 4000/ (1.732 x 400 x 0.8)
I= 4000/554.24
I= 7.21 Amps per phase
The problem I have is that the label on the pump control says that its rated current is...
i am just a little unsure if i need to use 5 seconds as my D/T or 0.4? PFC obtained through Ze test at origin.
i have been told 2 different answers and any guidance would be helpful.
thanks james
Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with one of my pieces to be assessed by NICEIC. I'm doing a full rewire at my dads house and would like to check that I'm calculating the cable volt drop...
Just a quick check to see if my math's are right for NVQ3 assessment.
Ze - 0.01 Ohms
Circuit length - 28m
CSA of line and cpc - 2.5mm2
Conductor material - Copper
R1=pL/A
R1=((1.78x10-8)x 28) / (2.5 x10-6)
R1=0.19Ohms
R2=pL/A
R2=((1.78x10-8)x 28) / (2.5 x10-6)
R2=0.19Ohms
Zs= Ze +...
Hi everyone just a little confused,when calculating volt drop using table 4Ab do you measure the voltage of the installation and use that value to calculate or do you just use the 230 volt value