Evening all
When doing a consumer unit change, how much dept do you all go into? Do you treat it like an EICR with 20% ish and spot checking?
Normally we do end to end, r1 or r2 and IR test once the old board is off and Zs when the new board is on. We try and find end of the line on each...
Hi guys. Just a quick question. If changing a board only and tails are in wall burried or in a cavity, am I required to change them if they are existing? Or can I note it on cert that they was existing? In my eyes they need changing as if in wall rcd protection is needed and if in cavity there...
Hi guys.
Looking for a bit of advice if poss.
Looking at changing a board as part of an assesment. Looking at the new regs it states that the use of type a rcd now should be used. But I have had conflicting info from others saying ac is still ok? I know type a is for the allowance of detecting...
went to change three smoke alarms today and found they were wired in 1.5 t&e useing the cpc as the interconect link wire.
would you class this as a c1 / c2
i was thinking c1,
any thoughts
Hi guys and girls,
Changed over my first CU today (didn't go bang so I'm classing it a success), with regards to the EIC do I list every circuit and fill it in as if they were new circuits, I've had a look at the best practice guide for CU's and the way i'm reading it it would suggest yes as...
Has anyone on here changed careers? Come off the tools, moved into a different field?
I’m still mulling things over like I have been for past year or so and I really would like some advice on this. I don’t feel that setting up on my own is an option for me and I’m not financially set up for it...
Working with a spark, now when we change a CU no new circuits just old for new, We do all end to ends on rings, IR tests and Zs making sure all the new protective devices that disconnection times are met, would you do R1+R2?
If we do a CU change and add new circuits we do R1+R2 on the new...
Hello all,
I'm currently a HGV driver but it's not something I want to continue to do. I enjoy learning new things and expanding my knowledge which my current job doesn't have.
I have always been interested in becoming a electrician and now at 25 I feel like it's now or never to actually...
Had to change 40 consumer units the other day in a hostel/hotel/b&b and it come to the testing stage
I spoke to the NICEIC who said you need to test circuits for " safety only ". He said doing a global IR test (testing each individual circuit if less than 1M), and earth fault loop, RCD and...
hi there just introducing myself. I’m 28 and currently looking for a career change to become an electrician. Going to get access to the trainee forum. I’m based in Glasgow any advice on where to start would be very much appreciated
Thanks
Steven
Hi,
I drive a 1999 Toyota Corolla.
I bought a new battery 2 weeks ago which was flat this morning. The battery warning light came on on my way home from work last night.
I jump started it and took it to the place I bought the battery.
They changed the battery I had bought for a new one...
Hi All. So i am 30 years old and thinking to change my career. At this moment i am working for a builders merchant as a manager and earning 28k, but I really want to change my career. Thinking to lear electrician trade, but not sure how to start and where to start. I have a family and i need...
Hi, I'm looking to replace my electric single fan oven. It is plugged into a double socket, the other socket having the gas hob plugged into it, and this double socket is wired to a 13a switched fused spur. Looking at the ovens in my price range I can see some that include a plug and can be...
Don’t do many fuse board changes, but what’s everyone’s preferred method, as I see people without labelling the old cables swap boards connect up neutrals and earths then leave line conductors last but how do they make sure each correspond to each other so you can identify the circuit like the...
I agree that it's best to do an EICR before a CU replacement, but is there an actual regs that dictates that an EICR 'must' be conducted prior to a CU change?
Hi all. im at a stage where i cant face getting up in the moring to go to work. ive tried jobs in commercial and domestic but i dont have the passion for them like i used to. ive been in the trade for 15 years including my apprenticeship but now im considering a totally different carrer.
I know...
I’m only an apprentice and of course, I’ve curios about a lot of things. I was in my friends house recently, who is getting an electrician to upgrade there, rather old, consumer unit up to 18th edition standards.
I had a look, out of curiosity and seen this (uploaded a photo) and I was curious...
I have a 2007 Nissan Pathfinder Aventura (R51) it is fitted with Xenon headlights. I want to fit european headlights as I am exporting the car to France but am unable to find the xenon headlights. Is it possible to change the existing headlights to Halogen? If so how technical is the change?
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc