just wondered how everyone else would code this lamp post.
the original installer made a type of swa gland from copper pipe and a BS88 clamp.
they also issued a 12 year inspection date.
its all just a thought exercise now as i have added a proper lamp post cut out with swa 20s glands.
The oven locked itself and the door so I had to turn off the power and can now open it again. Only thing is the oven is no longer heating up at all. I’m seeing an “F53 error” code is flashing up with a symbol of a key. I have looked at the troubleshooting section of the manual and it says...
Hi guys
Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the Regulation supporting this Code 1/2?
I can see 411.3.1.1 but this relates to Lighting. If anyone could assist Id appreciate it, I know its a fault but...
See this time after time - poor installation:
new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The board is metal and there are split load single insulated conductors before the 30mA rcd's.
If these conductors touch the metal work the board may...
A pull-cord shower switch is located in Zone 2 of a bathroom, including the ceiling base containing the electrical connections. With a little effort it may be possible to get spray from the shower onto the base.
I assume this is a C2, but wondered if anyone here might give it a C3, based on it...
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give for the following. The system used to be conduit & singles but was rewired in twin at some point. By the looks of it the conduits were cut at top &...
Hi
I am looking at where does my dishwasher leaking. I find there is some leaking at the bottom behind but not from the hose pipe inside , since i failed to upload video here so i just screenshot some leaking photos, your advice on which part should be look at or replace is highly appreciated thanks
Mileage: 112223 - DTCs - P0480 cooling fan. Also codes in TIPM P0691, P0692 for cooling fan control circuit.
Tests/Procedures Performed:
1. Using a Autel MaxiDas D808 compatible scan tool, I actuated the cooling fan relays with the ATM tests.
2. Removed the low relay from the Totally...
Morning,
Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking at high level. For reference, this trunking has been pre-drilled with 20mm holes at set distances on either side. Within this trunking is multiple...
Good afternoon - we're considering adding an additional breaker to our "main service panel" which is where the meter is located. That panel has 6 slots (I guess 12) with 5 double breakers currently. One breaker is 90 amps which feeds our interior panel which has lights, cook top, A/C condensing...
Hi all
Called to do an EICR on a property 4 studio flats / bedsits within a single house.
The t&e sub main to each flat runs within the fabric of the building and has a 30mA RCD at its distribution point...assuming this was an add on to the original installation.
Each flat has a RCD main...
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and probably closer to 280' from the utility connection on the far side of the home), which has a breaker box in it supplying three 20A circuits (lights on...
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket
second : Roof above bathroom has terrible leaks . Lights spark and buzz etc when raining .Video evidence shown to tester . tester says it not a C1 or C2 as its not...
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR.
Following items I found were;
Upstairs and downstairs smoke detectors mains fed but not interlinked, on separate circuits.
downlights open backed and clearly not fire...
Morning All
Qualified electrician, usually stay away from alarms but my friends parents have issues.
Texacom Vertas panel, not worked for over 3 years (since they had the front door changed.
Located the cable and linked out to see if this overcame the issue, it did.
Problem now is that the...
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb.
I know this is bad practice to install unless using bigger SWA to achieve required csa's in awkward spaces to terminiate.
My question is what code is this? Im...
With regards to Regulation 531.3. 3 of BS 7671:2018+A2:2022
Older AC type RCD's are prone to being blinded by dc leakage from other items plugged in to the property. In other words this RCD may fail to operate when other electronic items are plugged in which leak DC in to the mains.
Regulation...
Please skip to the next paragraph to skip my intro.
Sitting at a desk is not how I want to spend the rest of my life, so I've decided to become a mechanic.
They say "if your job is your hobby, you'll never work a day in your life."
I've always enjoyed resurrecting things that others deem...
Hello guys n gals,
Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run.
The 8.5kw shower had been replaced by the tenant for a 10.5kw one (old one was still in the cupboard is how I know).
Unusually, the installation supply...
Hi,
Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario...