Hi
My smart meter stopped communicating last September with the IHD and my supplier Bulb. On the actual meter it permanently shows V38.03 10.02 and on the bottom line b2Y5530 neither the A or B button have any effect. I have been chasing up an engineer visit since last year but apparently...
OLEV audit what a joke
Our audit was fine however the Niceic accredited auditor gave us a code 2 for putting the cat 5 cable through the same gland as the twin and earth supplying the charge point.
The manufacturers data states the data and power can go through the same gland in a photo as...
I wonder if you can help I've just had a EICR on a property and I've received a C2 due to the fact the down-lights aren't IP rated. Having sat the BS 7671 some years ago the BS tells me that the zone 2 height is 2.25m. The ceiling in question is 2.3m. Appreciating it's advisable and I'll swap...
Hi all new to form so thought I would as a question.
Testing a final ring circuit & all is normal apart from the live / brown legs of the circuit which are too short to reach the MCB so they have connected them together in a block & extended it within the CU via a 6mm to the MCB
Just wondering...
Hi,
I had what I thought was a licensed electrician extend electrics from an outlet to the opposite wall for lights in a wardrobe I'm having installed. The wardrobe builder requested a fixed spur on the wall and the cable to to be run under the floor boards.
However, the electrician ran the...
New to the forum
I took classes when I was a bit younger and was on track to join the electrical trade and then changed course.
I have done my own personal electrical work for years.
I am a general contractor working in southern Oregon. I work a lot with owner builders doing consulting...
During a inspection and test of low rise flats communal area i found the door entry system has single insulated and possibly touchable conductors or terminals .
in the past i have coded these either C1 or C2 depending on live conductors being touchable.
they have now built a large wooden...
Mainly on commercial lighting with twin and earth 1.5mm or 1mm on 6A and 10A type C breakers
Im sure there was a table in bs7671 requiring larger CPC sizes for type C breakers than supplied with twin and earth, hence why people use fb200 or singles etc
I guess it must be restrictEd by let...
Doing an inspection and came across this.
Feeds are as follows:
Cutout to Meter - 25mm
Meter to connector blocks - 25mm
Connector blocks to CU’s (2 in the house) 16mm.
So far so good as the cutout is 80A not the 100A it’s labelled as.
My query is the 6mm 3 core XPLE that’s going to an...
Hi guys I really need some help on this question. semi enclosed fuses are located in a distribution board where Ipf was measured and recorded as 4ka. What code would be given during a periodic and does and what is the associated regs number for it?
THANK YOU
Hi All. My company have a brand new and supposedly unused FLUKE 6500-2 appliance tester, which i am unable to get into the settings, due to the ACCESS CODE, not being 9999 as i assumed it would be. I have also tried reset code of 1785 which was also suggested. But this is also not working.
I...
Since Electrician's forums are promoting this as a wiring example :
What code should it be given
C2 for exposed insulation
C3 for device not in its enclosure
C2 for no earth/CPC
C3 for wrong wiring colours
C2 for incorrect identification of line conductor
C3 for mixture of devices (if there...
Originally one all the bedrooms had plaster ceilings. In one bedroom someone added firing strips and installed acoustic ceiling tiles on top. The ceiling tiles were removed during renovation and then a licensed electrical contractor ran Romex along the firing strips to the center light and...
On a test & inspection today, I came across an older Wylex split load board that had been modified to add RCD protection for all circuits (see photo). The main switch was replaced with an RCD (despite there being room to add the second RCD to the left of the main switch). So a fault (or RCD...
Another what code!
This is in conjunction with an EICR I have just carried out.
9.5kW shower on 6mm and 32A MCB. Been in place for a long time, no signs of thermal damage in CU or 45A shower pull switch. Ref method C (where visible in loft), unable to clarify ref method where it is buried in...