Scenario:
3 phase DNO with 100A fuses into a control unit feeding 2x 5kVA txs with combined load of 40A.
We're adding 2 more 5kVA txs, one with 14A, the other 21A.
What I've come up with so far:
63A fuse consumer side will need replacing with an 80A BS 88-2 (gG) fuse (max Zs 0.57Ω)...
Hi All
I am going to be installing some high bay lighting which will consist of 3 x 400w metalhalide fittings so 1200w in total with runs of approx 60 meters in 2.5mm cable. I will be wiring the circuit via a 20amp contactor with a control circuit of a two way switch system to activate or...
Correct me if I'm wrong but ..... To become an electrician in the UK
I have completed an apprenticeship and continue to be working for a local company going on 5 years total now.
I did 3 years in college, plus 2 years on site experience (NVQ level 3)
Also did AM2 (what's the point if not...
Hi All,
I'm new to the site, so hello all.
I've only managed to find old postings to my questions so i'm hoping someone can help.
I'm looking to move into property development, and its making me wish more and more that i had studied a trade at college. Im know looking at doing a course at...
Hello All,
First post.
So, I have designed the following setup:
The question is, does it look okay?
The RCD FCU is on a ring main, using 2 cores for earth from the FCU to Outdoor socket box.
Cheers...
I need to put an extractor fan in a small downstairs toilet with no window. I know it has to be fused to 3amps and I know it has to have a run over facility, and that it must be linked to the light switch/switch to conform to building regs. It will be a staff toilet and I am aware that people...
Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with one of my pieces to be assessed by NICEIC. I'm doing a full rewire at my dads house and would like to check that I'm calculating the cable volt drop...
fire8789
Thread
calculating
correct
length
main
please
ring
ring main
voltage
voltage drop
volts
Hi,
I want to wire up a 12V DC timer (CN101A) to turn an appliance on and off. I have the found on the internet the following wiring diagram for the timer and not being too experienced I was wondering whether it will work if I make the connections as shown:
The timer does not show + or - so I...
We seem to be getting conflicting answers on whether the recommendations in Part M relating to installing sockets and switches at 450mm to 1200mm respectively also apply to existing dwellings undergoing a full refurbishment (and rewire). Can anyone put the record straight?
BC are involved on...
Anyone with experience of this or an idea please help.
I have 2 phases going going into a cab, each one 230v. However there is a real chance someone could touch the two and get a belt from each phase at the same time.
What would be the correct type of warning sign to use? Also out of...
harrison2987
Thread
correct
help
high voltage
off
phases
please
voltage
volts
warning
I have to do an install using trunking which I have nebr used before, I understand there had to be 45% free space inside for heat travel.
so what size trunking do I need to fit two 2.5 t&e cables inside?
As I said I have never used trunking before so it is new to me.
i have had a few solar panel quotes where one guy has said a ten percent year on year rise in electric one at 5% one at 7.% and this makes quite a bit of difference to my returns who do i believe and who's is the more accurate figures should they not all be using the same increase percentage...
Hello all. I'll start by saying this is my first post. My name is John and I'm a maintenance engineer (electrical) from Scotland. Have found alot of cooker info on here but just to make surey My fully electric cooker is rated at 12925w and there is also a 45a fuse protecting and 6mm cable...
Hi i was looking at this old post and saw a calculation resolved which im not too sure is right and would apprciate confirmation wether it is or isnt
Q24. A continuity of ring final circuit conductors test is to be carried out on a circuit supplying the office. The circuit is wired in 2.5mm...
Hello all..
I figure its better to ask and be ridiculed than not!
I am about to add a couple of spurs to a ring that is not RCD protected. The neighbour definitely wants them channeled in rather than surface trunking so I have to RCD protect. It is an old Tenby CU with crabtree SB6000 MCB's. I...
hi all, can someone if the following answer is correct. would as teacher but 2 days till class.
a coil of inductance of 0.2H is connected across a 230V 50Hz supply. What will be the current flowing in the circuit, if we assume that there is no resistance?
XL= 2pie fL
XL= 2pie * 50 * 0.2 =...