cpc

  1. K

    Continuity of CPC at Ceiling Rose

    Had to leave a job early tonight, so couldn't resolve what should be a simple issue, but now it's buzzing round my brain. I have 5 ceiling rose's and pendants in a good old loop system. All 1 Way. I have good continuity readings at rose numbers 1,2,3 and 5. I have good continuity...
  2. P

    Old single sockets, unsheathed cpc.

    Hi all, looked at a job today to replace 5 x single sockets to 5 x doubles. Looks like the CCU was changed maybe 4 or 5 years ago but no paperwork - the property has the old wiring in place - red, black and unsheathed cpc. The single sockets are only 4 inches from floor level so i will need to...
  3. BigSi

    NICEIC Certification Scheme NICEIC’s Connection magazine (using CPC as a live conductor)?

    I was reading the latest issue of the NICEIC’s Connection magazine, when came across an article about wiring extractor fans. I didn’t read it in depth (was in the library at the time!!!), but from what I can gather you can now use the cpc in a flex (flex only, not hard wired) as a live conductor...
  4. K

    Who need cpc continuity?

    Was helping a fiend to change some socket outlets, standard white to brushed steel in her kitchen. She only had the house re wired 2 years ago - got the part P paperwork. This is what we found behind one socket. WTF was the bloke thinking?? Also obviously doesn't bother with grommets. I also...
  5. L

    Use of cpc as a live conductor - EICR Coding

    Fella's I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that...
  6. S

    CPC - Neutral Fault

    Hi Ive just changed a Consumer board and fitted a Wylex split load,5 Rcbo's one side and 4 Mcb's on the Rcd side. After connection of all conductors (all in correct terminals) it turns out one leg of my ring has a faulty Cpc, i've carried out an IR test and there's an issue with the neutrals &...
  7. J

    Calculate the min size of cpc giving consideration to disconnection times and thermal

    Hi everyone, On the drawing it says the system's TN-C-S with declared Ze = 0,008 Ω and prospective fault current declared as 50kA When I calculate If = Uo / Zs = 230 / 0,716 = 321 A . With this value there's no way to match with 10A curve at fig. 3A6 (appendix 3) But if I calculate the...
  8. N

    In what context do you use a CPC?

    Gentleman, Im reading through the forums, especially the fault finding threads in this sub and there are a lot of talk about CPC's. when someone has time could you please explain what a CPC is and when it is used? im sorry if this sounds like an amateurish question but its because at this...
  9. M

    cpc

    Hi guys. Correct me if I'm wrong your cpc and earthing conductor should be no less than half the size of your line conductor.
  10. M

    15v on cpc

    Hi all I'm struggling to get my head round while I'm getting 15v on the ring main cpc, but when I turn the lighting circuit off it drops to 0v can any1 else work this out.
  11. B

    Equivelent CPC sizes for metal trunking

    Hi Im looking for a table that gived the equivelent cpc that a metal trunking would provide. many thanks,
  12. TaffyDuck

    Voltage on CPC from PV Array.

    Hi Guys I wonder if someone with more experience of PV might be able to give me some advise. Was called out today to a domestic building with a remote barn on which a 4kW PV array is sited. The Inverter is in the barn and a long (50m) 2.5mm twin and earth in pipe (historic) feed back to the...
  13. W

    No cpc to lighting circuits

    Went to change a light for a local estate agent today, No cpcs to the lighting circuit would i right right if i said the circuits would have to be rewired?
  14. B

    Final ring circuits with radial CPC

    Have justed looked at a job to replace the consumer unit and it appears that both the final ring circuits ( Kitchen and the rest of the Flat ) have Radial CPC's. The flat is wired in multicore Singles and Plastic Conduit , has anyone come across this type of design before. Both "ring circuits"...
  15. Rockingit

    6mm integrated CPC of 16mm 6242Y used for main earth

    My adiabatic maths says that for a 16mm main conductor, assumed Ze of 0.2, 80A 88:3 CPD, k as 115.... the earth only needs to be 3.16mm therefore the 6mm in a 6242YH 16mm is more than sufficient. Anyone disagree?
  16. S

    Consumer Unit Change - No CPC on lights - Borrowed earth

    Been asked to change a consumer unit On inspection found out that customer had done much of the work himself - approx 20 years ago Currently has old Wylex NN Board Ring Mains & Kitchen appear OK - T&E Lights have no cpc, except for a couple with metal fittings. The lights with metal...
  17. B

    Insulation resistance testing with no cpc

    When doing a CU change and lights have no cpc. Every room has class 2 dimmers and lights. ceilings are like 20 foot tall. How would you guys go about Insulation testing? L&n to cpc ain't an option and removing all lights and bypassing dimmers is consequently going to take some time... What would...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top