cpc

  1. P

    class 1 light fitting with no cpc

    Been asked to swap over a class 1 fitting for another old existing class 1 on a first floor hallway - however there is no cpc on the light circuit! (early 1960s house). In the loft there is a rfc junction box close at hand. What about putting a 4mm g/y single from the light fitting to the J.B...
  2. B

    sizing SWA armour as cpc using adiabatic......

    I'm doing a mod for a 3 phase circuit already installed. The only trouble is I can't work out why the existing cables are as they are so i am doubting my sums. Existing final circuit. 3 pole memshield 2, D32 rated feeding 10mm2 4 core swa with a seperate 16mm2 G/Y as cpc. Measurements at the DB...
  3. S

    minimum cpc sizes

    Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083 Circuit 1L1 Assuming we can use 1.5mm cpc R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms...
  4. 1Justin

    no CPC on lights, - switches for class 2?

    I'm looking at the options for customer who has no CPC on lights as is quite common. I know the ESC "good practice guide" - and that all makes good sense. However most light switches with exposed screws into metal back boxes (where metal box is unearthed because no CPC), would therefore be...
  5. P

    Board change with no cpc on lighting

    Hi all Been asked to quote for a board change. Had a quick look round the place and discovered lighting circuit has no earth. Where do I stand on this? Current board is 3036s and will be replacing with rcbos as wiring is quite old. Will also be bonding the gas and water from 4mm to 10mm.
  6. K

    Continuity of CPC at Ceiling Rose

    Had to leave a job early tonight, so couldn't resolve what should be a simple issue, but now it's buzzing round my brain. I have 5 ceiling rose's and pendants in a good old loop system. All 1 Way. I have good continuity readings at rose numbers 1,2,3 and 5. I have good continuity...
  7. P

    Old single sockets, unsheathed cpc.

    Hi all, looked at a job today to replace 5 x single sockets to 5 x doubles. Looks like the CCU was changed maybe 4 or 5 years ago but no paperwork - the property has the old wiring in place - red, black and unsheathed cpc. The single sockets are only 4 inches from floor level so i will need to...
  8. BigSi

    NICEIC Certification Scheme NICEIC’s Connection magazine (using CPC as a live conductor)?

    I was reading the latest issue of the NICEIC’s Connection magazine, when came across an article about wiring extractor fans. I didn’t read it in depth (was in the library at the time!!!), but from what I can gather you can now use the cpc in a flex (flex only, not hard wired) as a live conductor...
  9. K

    Who need cpc continuity?

    Was helping a fiend to change some socket outlets, standard white to brushed steel in her kitchen. She only had the house re wired 2 years ago - got the part P paperwork. This is what we found behind one socket. WTF was the bloke thinking?? Also obviously doesn't bother with grommets. I also...
  10. L

    Use of cpc as a live conductor - EICR Coding

    Fella's I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that...
  11. S

    CPC - Neutral Fault

    Hi Ive just changed a Consumer board and fitted a Wylex split load,5 Rcbo's one side and 4 Mcb's on the Rcd side. After connection of all conductors (all in correct terminals) it turns out one leg of my ring has a faulty Cpc, i've carried out an IR test and there's an issue with the neutrals &...
  12. J

    Calculate the min size of cpc giving consideration to disconnection times and thermal

    Hi everyone, On the drawing it says the system's TN-C-S with declared Ze = 0,008 Ω and prospective fault current declared as 50kA When I calculate If = Uo / Zs = 230 / 0,716 = 321 A . With this value there's no way to match with 10A curve at fig. 3A6 (appendix 3) But if I calculate the...
  13. N

    In what context do you use a CPC?

    Gentleman, Im reading through the forums, especially the fault finding threads in this sub and there are a lot of talk about CPC's. when someone has time could you please explain what a CPC is and when it is used? im sorry if this sounds like an amateurish question but its because at this...
  14. M

    cpc

    Hi guys. Correct me if I'm wrong your cpc and earthing conductor should be no less than half the size of your line conductor.
  15. M

    15v on cpc

    Hi all I'm struggling to get my head round while I'm getting 15v on the ring main cpc, but when I turn the lighting circuit off it drops to 0v can any1 else work this out.
  16. B

    Equivelent CPC sizes for metal trunking

    Hi Im looking for a table that gived the equivelent cpc that a metal trunking would provide. many thanks,