No photo's as customer is already in dispute with kitchen fitter and was very strict about it!
I went to look at what would be involved to add a missing dishwasher point in a brand new kitchen.
House is TT. Kitchen is on a B16 radial. Hob and Cooker are on their own circuit. It's only sockets...
I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system before it is sent to an event where people like me with 7909 then plug in and do some basic testing.
I've completed 7671 and other domestic install...
In the market for a flexi-coil high rated current meter, wondering if anyone has used one of these before? Or has an alternative recommendation.
https://www.test-meter.co.uk/chauvin-arnoux-digiflex-ma4000d-350mm-sensor
I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data sheet says it’s current carrying capacity is 136amps. The lengths will be 0.5m.Is there any other consideration I should take into consideration? It will...
How do I limit or feed inrush current for higher constant current use?
If I could find solution, then the chosen battery cell type can have much lower Discharge/Charge rate.
My product research found that lower Discharge/Charge rate cells are much lower price.
So you can purchase more storage...
Had one today I can’t get my head around. 4Kw motor connected to an Allen Bradley soft start. The panel runs 2 motors Both 4kw. I was called originally due to one motor not running. This turned out to be a tripped the motor circuit breaker (one with adjustable current dial). I tested the rest of...
Hi guys, I expect this topic has been covered before, In rented accommodation including business premises, should the electrical installation be up to current BS 7671 Regulations.
During a recent EICR the RCBO keeps tripping , i measure leakage of 2.6 ma when clamped around line and neutral, when i clamp the cpc i get over 10 ma ,its a PME supply 0.09 ZE.
These RCBOs have a functional earth , the RCBO ramp tested at 21 ma .
does anyone have any idea why this is...
hi, new to this forum and still training. During testing for prospective fault current at the point I get a bad reading, what ever that may be????, what possible situations would be causing and why? still trying to get my head round it...
thanks Adam
This week I nearly learned a hard lesson re this!! (using a Lutron RA2 inline dimmer to control 6x 700ma 13w LED fittings)
https://www.lucent-lighting.com/site/assets/files/6952/2605-cb-tl-1.pdf
So I thought 6x 13w=78w- thats fine its well within Lutrons stated 150w of LED load.
But after having...
Hi
Looking for a bit of advice on a led driver
The Aurora in the picture below is the one that needs replacing today / tmrw
And the only 700ma constant current driver I can find local has slightly different specs DC 16.5v max on the original
33 - 40v dc out on the new one
Will this work...
Hello,
What happens if we use disconnect switch over its operating curent Ie?
For ex.
If our circuit is motor circuit and current range is 140A. We need to use 160A. But we used a disconnect switch with operating current Ie as 125A not 160A.
Making and breaking capacity of a disconnect...