I have been to look at a job this morning to rewire a radial feed supplying two socket outlets off a 20 mcb. The cable from the board is a black pvc 2 core cable(does not look like copper) and has a separate earth run back to the met.
I am currently doing my 2392 and hope to start...
Hi
Do any sparks know of a product that will clamp better to earth bars at consumer units and accessories. I’m getting tired of my croc clips slipping off when testing, especially when trying to zs a light 3 plate. I’m thinking there must be something that will grip around the screw that I can...
(Rented property) The current bonding under the sink is 6mm - the electrician said it has to be min 10mm in order to pass the EICR.
Is this correct? It looks like the wire has been there since the house was built and electrician said he would have to take a new one from the fuse box and somehow...
Sorry in advance. Didn't sleep well last night and my brain has haemorrhaged!
Just designing power to a shed with 3 floodlights on the lawn from it (swa underground) and I was going to use some metallic spikes to bolt the lights onto but I'm thinking now that would mean an earth rod having to...
Seen loads of flats are fed from a 60amp isolator in 10mm twin and earth?
don't they need to be 16mm tails and at least a 10mm earth?
or is it just down to the adiabatic?
Come across this a couple of times recently whilst doing eicr’s. Everything all ok except there is no access to the (presumably) earth rod. The cable just disappears under a patio.
Of course it may not even be an earth rod. It could be a plate or something. I’ve been giving these a C3 as I...
TT system, Zs on socket circuit is 77.2 down a good bit after I added a second earth rod.
When I short neutral to earth RCD doesn't trip.
Can anyone help me out and explain please.
Hi, just wondering how other sparks, go about confirming main earth bonding continuity when supply cannot be isolated, ze and pfc can be enquired wich is fine but what happens if you cant disconnect main bonding earth, is previous test results good enough to confirm?visual checks good enough...
So I recently installed a new circuit to my loft as a dedicated burglar alarm and cctv circuit. When checking polarity and voltage with my test lamps/voltage indicators it didnt trip the rcd when testing live to earth and neutral to earth. It's an rcbo which works when using the functional test...
Hi all I bought this light online, says it's suitable for 240V. The cable it came with only has live and neutral no earth, however as you can see in the pics it has aluminium brackets for mounting, it also has what looks like aluminium backing and screws but these feel like they're made from...
Hi all. First post.
Earth rod question. All work I've done, as a recently qualified DEI has been on tncs. Have a new job with TT. Old earth rod is buried under concrete steps. So I have installed additional visible 2 m rod and run new 10mm earthing conductor. I have a fluke 1662 and recently...
UK. Domestic computer setup with uninterruptible power supply - APC brand devices BK650EI and BK350EI.
The manufacturer offers almost no information on earth and I presume that protected appliances are on their own independent circuit. Modest testing (ordinary multimeter) suggests there is no...