    Eicr code

    hi all, done a eicr recently and found the following and would like thoughts on the codes? Thinking code 2 but bit harsh to fail the installation on these points esp as its been like it for 30 ish years and no problems or atleast that's what the owner will say!! Cpc used as live on landing 2way...
  2. D

    EICR code

    I'm doing a EICR on a caravan site. Came across 5 circuits each supplying about 13 16A socket outlets. All are protected by 63 A mcbs and all wired in 6mm twin armoured cable buried underground. The cable rating for the cable is 46A with the ref installed etc. Im undecided if I should code 3...
  3. E

    EICR code - potential load on lighting circuit more than MCB rating

    I'm writing up an EICR. On one of the lighting circuits the potential load is theoretically about 1300W on a 5A BS3871 breaker. In reality, the arrangement has been in place for at least 8 years there are no signs of thermal damage, it is difficult to find lamps these days that would max out all...
  4. N

    EICR code

    Hi can someone confirm what code you would give metal light and sockets with no flying earth to the back box. Lights are on a non RCD side of the board so was unsure if it's a C3 cheers Neil
  5. S

    EICR Code help

    Just tested a bungalow and fond the power is all supplied by one radial 2.5mm circuit rated at 32A on a fuse not MCB. Was thinking C2, there are only 15 points in the on the circuit and most re not used. will be carrying out a full rewire in a couple of weeks any way. If I reduce the fuse size...
  6. B

    cable outside zone. is it a big deal? EICR code?

    A 10mm cable supplying shower is chased down the bathroom wall (in correct zone) and is then chased from celing height down the wall in the kitchen below. The cable pops out of the kitchen wall below contertop level making the rest of the journed to the CU on the surface but cannot be seen...
  7. J

    EICR code for non metal fuseboard

    Hi all Does anyone know what code on an EICR we are to use for a non metal fuseboard in a dometic premises? Thanks
  8. G

    Eicr code

    Ring main wired in 2.5mm singles but only one cpc conductor. What code would you give?
  9. G

    eicr code

    about to do a remedial job, another contractor has given a c2, to basically a domestic db, tails come in from cutout into main switch of db, their is also another set of tails from that side of main switch to an adjacent db for a shower circuit. I cannot see a code 2 on this? Maybe a c3 as best...
  10. H

    EICR Code

    Would a C3 be adequate for a main protective bonding conductor connection to water not readily accessible? Connection is present (along with tag) but is under floor boards. Took me ages to trace it back. Also I can not verify the location of the gas bonding connection. What code?
  11. W

    Potential Eicr code opinion please

    2x 3kw extraction fan motors with no starters or O/L cutouts, switched on and off direct via rotary isolator is it even to be coded? would like any opinions please
  12. G

    Ccp eicr code

    2.5 mm radial t&e supplying 2 twin sockets on 32a Rcbo. Code2? 6mm radial to heater three phase nny-j cable, ccp of 42a on 50a mcb code 2? 2.5 mm radial t&e supplying one ac unit 32a mcb code2?
  13. N

    EICR Code C3 Meaning

    Current GN3 p.80 says C3 means "Improvement required". Current GN3 p.105, model EICR form, says C3 means "Improvement recommended". Your thoughts? Bit of a cock-up if you ask me.
  14. M

    EICR Code for no main earth

    Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
  15. H

    Help with EICR code!

    Hi, just wondered what your thoughts are on this, 3 bed town house Whole house ring final, mixture of 2.5 / 1.0 & 2.5 / 1.5 twin and earth cables, End to ends = 0.78, 0.78, 1.6. R1r2 = 0.61 (spur). ZS = 0.66! BS7671 recommends a max of 100 square meters which using 2.5/1.5 = an r1r2 of...
  16. jibjob

    Boiler in bathroom EICR code

    Hi Guys, Came across this today in what seems like a newly refurbished bathroom. As you can see from the picture (hopefully) is that the boiler is less than 600mm from the edge of the shower enclosure. Not sure what the IP rating of the boiler is but the adjacent switched connection unit &...
  17. G

    Eicr Code

    6mm singles from 100a TP 60947-2 in a main panel to an adcent enclosure to a 16a 60898-D Tp, then 6mm leaving this to air con units. Would you code 2 the 6mm singles from the 100a 60947-2? As exceeds current carrying capacity?. Or because the 6mm singles are less than 3 metres to the enclosure...
  18. H

    TT eicr code?

    Hi doing an eicr on a tt system, plastic board, bonding ok! It is a split 16th edition board with 80amp 100m/amp main switch which has the lighting, smokes and boiler on. On the other side is a 63amp 30m/amp rcd protecting sockets, cooker and shower. The Ra is 28 ohms. anyway my interpretation...
  19. H

    EICR Code Help!

    Hi just after a quick bit of guidance, I have completed an EICR, and found a spur of a spur on a ring final circuit, there were no signs of thermal damage and the sockets are in 2 bedrooms and feed table lamps and phone chargers. I know this is a no no in terms of the regs, but what would...
  20. B

    EICR code

    Hi Guys had to do an EICR today for a job on which the installer hadn't certified. Everything was okay but I didn't know what code to give for the following; the immersion was supplied via off peak supply on its own circuit but the top element was supplied via the ring main? I remember...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Back
Top