  1. newfutile

    C2 or C3 on recent EICR

    During an inspection i have come across a class 2 light fitting with a cpc that’s is not connected to MET. initially i put this as a C2 but I’m wondering what others thing? where is the danger as it is?
  2. K

    C2 rating on EICR test report

    Hello Everyone, We are looking to buy this house but the EICR report have a couple of C2's. Any help advice on these is much appreciated. 5.11 - Provision of additional protection by RCD not exceeding 30mA For mobile equipment not exceeding a rating of 32 A for outdoor use only 8.0...
  3. LandlordSafetyCertificat

    I Need Work New to this forum and with more than 10 years experience

    Hello everyone, We are new to this forum and providing our electrical services in London and M25 area for last 10 years. Looking to get more clientele. Thanks LSC
  4. L

    what do you think of this EICR ??

    Another classic ....
  5. R

    R1,R2,Rn versus r1,r2,rn continuity readings on EICR.

    Looking at the EICR form. GENERIC SCHEDULE OF TEST RESULTS Looking for clarification on R1,R2,Rn versus r1,r2,rn continuity values. I have reached the some conclusions. Do r1,r2 and rn only apply to ring circuits and R1,R2 and Rn (not on form) to radial? It just looks like that might be the...
  6. D

    EICR code for hybrid final ring cir

    Hi all new to form so thought I would as a question. Testing a final ring circuit & all is normal apart from the live / brown legs of the circuit which are too short to reach the MCB so they have connected them together in a block & extended it within the CU via a 6mm to the MCB Just wondering...
  7. Spaniel

    Watch out for 300 EICR.

    There is a very active bunch of people offering 300 EICR's in your local postcode. SP in my case. Sky Home Maintenance, clever because if you search this all you get is the satellite TV people, used to be Legislative Property Maintenance and over 3000 companies before that. Have recently...
  8. C

    Hi, im new to this. I need some advice. Eicr

    I did an EICR and as I was doing the RCD trip times the circuits tripped as they should but then as I turned it back on the upstairs lighting stayed off (the breaker for the circuit is on) there is power coming out the circuit but none of the upstairs lights will switch back on. If anyone has...
  9. E

    EICR testing and inspection

    Before anyone asks I am a qualified spark.. been off the tools for years and getting back into it.. In regards to EICR’s it’s been a while.. Acceptable to add R1 R2 to Ze for ZS or do you all test all 3 anyway? I know it’s not acceptable to ZS and take off ZE to get R1 R2..
  10. I

    New MFT, what's the best units to look at? EICR industrial, time saving!

    Hi, I've just landed a job as an electrical tester and need a new MFT (mainly light industrial). As I'm going to be spending considerable time testing I thought I'd ask about the new high-end options. what are peoples favourites? Are these new fancy options like Bluetooth on the mergers...
  11. HappyHippyDad

    What codes for this EICR?

    I just have a question about the RCCB seen in the picture below. It is a 63A RCCB protecting the 32A shower circuit, 32A cooker circuit and 2 x 32A socket circuits. My concern is that the rated current of the RCCB is being exceeded. Even with diversity applied it is >63A. I realise we see...
  12. I

    My first EICR and I'm confused! I'm industrial this is domestic

    Hi, I'm an industrial spark and taking my 2391 next week (wish me luck, I need it). I decided to get a bit of practice and started an inspection on my own house. I got as far as, b32 socket (ring?!) breaker looks slightly browned, better check it. 3 cables in the breaker two identical and...
  13. S

    failed EICR, please can you advice

    Hi . I have a EICR that has failed . Can anyone please advice if some of the suggestions on there are legal requirements or not as there was an EICR on the property in 2014 and there was no problem with some of the things recommended in this report. For example : 1. -Remove & install new LED...
  14. littlespark

    “Can you do a quick EICR before end of year?”

    Picked up the keys this morning and had a quick visual… will do the actual testing on Monday… but what I’ve found so far…. (Not necessarily leading to anything worse than a C3) Missing pendant. Pendant in bathroom, non splash proof panel heater in bathroom, no fan isolator in bathroom…...
  15. newfutile

    EICR code for communal area

    During a inspection and test of low rise flats communal area i found the door entry system has single insulated and possibly touchable conductors or terminals . in the past i have coded these either C1 or C2 depending on live conductors being touchable. they have now built a large wooden...
  16. N

    Can an EICR be unsatisfactory with only C3 codes?

    I recently had and EICR done and received an 'unsatisfactory' report due to not all circuits being RCD protected on the consumer unit. The consumer unit was installed in 2007 and complied with all wiring regulations at the time (image attached). Does it need to be upgraded? I have attached the...
  17. E

    Cost of a commercial EICR

    Hi, I know a public forum isn't the best place to seek advice regarding "How much do you charge" chat but I recently did an EICR on a business property (Bar & Restaurant) I carried out the EICR when they were closed through the night. 3 boards, roughly 26 circuits total. No previous reports, no...
  18. W

    EICR code - type C breakers with undersized CPC

    Mainly on commercial lighting with twin and earth 1.5mm or 1mm on 6A and 10A type C breakers Im sure there was a table in bs7671 requiring larger CPC sizes for type C breakers than supplied with twin and earth, hence why people use fb200 or singles etc I guess it must be restrictEd by let...
  19. C

    Doing and signing of an EICR as an improver

    Hello! I am curious as to what the exact rules are in England for carrying out and signing off EICR's. I am finding different answers across google and various forums, some may be outdated, some may be bullshi. I myself have over 12 years sparking experience but I am just finishing off my...
  20. F

    EICR unsatisfactory but was the report/ testing carried out also unsatisfactory?

    Hi, hopefully, you can help me by giving some guidance over the EICR which has failed for my rented property. It was carried out by an electrician who is supplied via the managing agency. The first contact I had was an email that stated the EICR had failed and some remedial work was required...