Can you get the zs by using a earth loop impedance tester. I was taught if there's 2 rings circuits, you can do r1,r2, rn /4 on 1
On the other ring you can plug in the earth loop impedance tester and measure the zs. If you do it that way you must write in the observations you measured.
Have I...
Hi,
I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests.
I know parallel paths could cause a low reading, but...
Hi all,
Any advice on where to locate a manual call point in a commercial premises (shop) if there is nowhere either side of the entrance or close to where one can be positioned - or what have others done in the past?
Thanks.
Hi there all,
I have a property and I have noticed the following wiring (please see below) in one of the rooms in the house.
It looks like the ring circuit has been extended.
A single 2.5mm Twin + Earth cable (in red) is providing power from the consumer unit which feeds a chain of electrical...
Initial fault was RCD tripping, narrowed down to a ring final cct.
IR tests on that cct with all loads removed were showing almost zero between neutral and cpc.
So I broke the ring apart and eventually found the nail through a cable, and got that all sorted.
Now its testing ok in as much as...
In a ring if there is a 30A screw terminal junction box in the ring one spur can be taken off this. The j box terminals have three cables in them.
Each cable in a Wago (or an in-Sure) has it own connection slot for each wire. This makes a difference.
Wagos are mini bus bars. If a 32A four...
As above,have deregistered for vat(I was in cash accounting scheme) and am filling in final return,end date 13/11/20.
It seems,I have to account for vat on sales invoices unpaid on 13/11.Do I enter the entire invoice details or just the vat
content for the final payment?Also for inputs,can I...
Evening all
Pricing a bungalow that has 300mm insulation in the roof, as im going to be wiring around the corenrs as much as i can and through the middle would you use 4mm on the ring final circuits?
I want to use 2.5mm radials for bedrooms and living room but my boss is old school and wants...
Just checking, what I think I already believe.
Doing a pre-install test of some outdoor sockets on a ring final. So far, confirmed bonding, incoming polarity, Ze and Pfc and RCD Test on circuit, everything fine and within regs.
However on testing Ring Final, Line came out fine (0.7), Neutral...
Afternoon all,
A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD is a 16a type B MCB. All testing has come back as expected for a Ring final that has been installed in 1.5/1mm and the measured Zs is well within max...
Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other...
Morning All,
Currently carrying out an EICR and going through ring final steps with the following readings:
r1: 0.31ohm
rn: 0.32ohm
r2: 0.03ohm
Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo)
When i...
Done a condition report on a old mains board, everything good apart from ring final, got 0.55 nn 33.7ll and 3.8 on ee, changed board to main switch and rcbos, carried out a full accessory swap on all sockets and fuse spares in house, found some bad practice, twisted lives, n and earth's, no...
Hi,
Extending a ring final circuit off a socket in the kitchen through the wall into the shed on the other side. I already have 7 core NYYJ 2.5mm cable and I was wondering if I could use that to go through the wall to a J/B then connect to singles in conduit which would add about 4 meters in...
Hi there,
I'm just trying to get myself into cable calc and my first hurdle is demand and diversity. I understand the majority of what is coming across in tables A1 and A2 OSG but I'm just struggling to clearly understand what I should be using for demand on a domestic 32amp ring final...
Hi, Im new to fault finding, Im on a job where there is no live to live continuity on the ring final circuit which supplys the sockets to the whole house, with new flooring recently installed I cant access the floors, im assuming there are many jbs because its a 1960s property, if I connect one...
Hi, I've sat my am2 practical today.
I have a question about the ring final circuit hopefully there is someone who can relate.
Is it crucial to wire the ring final a certain way? Ive bought 2 legs out, one goes into my closest socket which went down a bit of conduit and the other leg goes to...
I need to install some extra sockets in a kitchen. It's a single story ex-commercial kitchen. All the wiring is in singles in steel trunking in the loft space, with drops through steel conduit to the various sockets and switches.
I want to install an additional 6 sockets under the worktop for...
Over the last few days I have been stuck indoors because of the rainy weather. To pass the time I cobbled together my simple idea for a FRC live conductor break detector, ie break in L or N. I also have a working demonstrator for detecting a break in the cpc but I will/may post that another...
Hi guys. Need to change the fuseboard at my parents house but none of their final circuits have a cpc run to them. Obviously have an earth on the main incoming so I can get a 16mm earthing conductor up to my new 18th edition metallic consumer unit but they don’t want a rewire so none of the...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc