heat pump | Page 2

heat pump

  1. C

    Dimplex 3-phase Air Source Heat pump (with Heatmeiser Control manager)

    Dimplex 3-phase Air Source Heat pump comes with Heatmeiser Control manager. Selling for a Customer - this item was unpacked, placed into position and wired and plumbed in. It was never, however, used as the Electricity Supplier could not install 3-phase power to plot as agreed. This unit was...
  2. marksparky

    ground source heat pump!?

    hi folks have a job coming up to price and heating is underfloor via a gshp, single phase supply and running on econmy7 tariff i believe, i havent wired a heat pump before and waas wonderin if some of u hav any experience in this type or similar system and cud give me some pointers as to wat...
  3. E

    Heat pump

    This unit requires a internal and external mode of isolation, a spur inside and a rotary switch for the controls outside, being that some of this equipment is outside I assumed that an RCD protected circuit is required, the manufacturer warns against a 30ma rcd as the unit may cause nuisance...
  4. D

    Zs on ground source heat pump

    Test readings on ground source heat pump are showing R1 + R2 as 0.03 ohms, zs reading taken at rotary isolator for the pump is 0.27 ohms. Protective device is a 63A type d mcb, run of cable is approx 7 metres, wired in 16mm t & e, ze is 0.11 ohms, max for a type d is 0.15 ohms so i'm well over...
  5. R

    Nu-Heat Ground sorce heat pump boilers?

    Hi, does anyone have any experiance with ground sorse heat pump boilers by 'nu-heat'. Ive had a nightmare getting information just to first fix the cables between the controlls, tanks sensors and boiler. If Im totally honest, a heating system even with underfloor heating zones, or hotel systems...
  6. D

    sub db for heat pump

    hi guys, the company supplying the heat pump for the house i'm doing recommend supplying it with a sub db. the heat pump is 12kw. my plan was to run a 10mm t+e and a seperate 10mm earth wire from the consumer unit off a 50amp type c breaker to a 3way db adjacent to the heat pump and wire all the...
  7. sythai

    Air Source heat pump wiring...

    Has anyone wired up one of these before: Airsource heat pump? Thanks, Sy
  8. sythai

    Air source heat pump, solar and underfloor heating advice...

    Evening all.... More questions again, thanks in advance chaps. Basically part way through a job where they are having: Underfloorheating (wet system) Airsource heat pump Solar ... just trying to suss it all out, have hardly ever done any heating systems before, in at deep end here and...
  9. A

    Heat pump - Locked rotary amp vs full load current

    Hi all I'm running a supply to a customers new pool and have the spec from the pool people. In the heat pump section it states: 20A main supply fuse, but then states that the LRA is 66Amps, and the SLA is 14.3 Amps. Am I right that the LRA (locked rotary amp) is the startup current, and that...
  10. J

    Ground source heat pump help!!!!!

    Hi, having a bit of trouble at the moment figuring out installation of a ground source heat pump. The electricicty company have ran two supplies to a new build. One 240v and the other 415v. The 415v supply is for the heat pump. Has anyone out there got any information what so ever on...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top