higher

  1. whinmoor

    British Gas owner Centrica warns of higher energy bills

    Although obviously bad news for 99% of people, this may be helpful for the solar industry as people might consider how to deal with rising energy bills: BBC News - British Gas owner Centrica warns of higher energy bills
  2. D

    higher Zs with RCD

    When testing Zs for circuits which also have RCD protection, what figure do you record onto your test sheets? when you exceed the max value for a specific MCB, due to the rcd. Do you just use a calculated value or do you actually record the value that you get even though it exceeds the max...
  3. S

    Inverter reading higher kwh than meter ???

    Our inverter is reading about 6% higher than the PV meter. It shows we've generated 311kwh since installed whereas the meter only reads 290. Is this normal ? Im guessing it's probably due to cable/efficiency losses.
  4. F

    RFC - end to end on CPC higher than expected ( EICR code advice please )

    In the process of a domestic EICR. RFC, i'm getting L-L (0.11) N-N (0.11) cpc-cpc (0.48) had to take off all socket fronts anyway as i did not like what i saw on a couple of random selected s/o & i've tightend up any loose cpc terminals i can find. I'm guessing that there could be a JB with a...
  5. S

    Customers **** me off

    Quoted a job and while back but customer didn't have funds available. ( customer is known to us through my engineers mum) Told the guy that I would requote when he was ready etc and chased up for the deadline EPC coming in. Anyway, it worked, money came in for him, bit of negotiating, email...
  6. S

    3rd march confirmed for higher fit rate

    source businessgreen confirmed 4-0 descision
  7. brucelee

    Zs higher than calculated

    Hi all I have a megger 1552 and when carrying out a Zs on socket outlets using the 13A plug in adapter my measured Zs was higher than my calculated using the No trip setting because of RCDs i was expecting lower due to resistances in parallel due to bonding when using this adapter should the...
  8. S

    8 commercial units, 8 meters on one set of deeds?

    I have been to survey a job and whilst discussing potential options we discussed a 50 kWp system on a barn and a 3 - 4 kWp system for each commercial unit. I feel that because each unit has its own meter and has its own user(s) it should be seen as 8 seperate systems all with the higher FiT...
  9. C

    Grid supply voltage too high!?

    We have a 29.76kw system of REC 240w panels. Feeding 2 x SMA 1500TRL Inverters. Supply is 3 Phase. Input voltage is around 250v constantly, peaking higher at times (we are positioned close to a new sub station). Our electricians/installers have had permission, from DNO and SMA, to raise...
  10. yellowvanman

    Higher wattage panels?

    I notice in Sunny Design there are some panels that go as high as 300W, anybody seen or know of any suppliers that have panels >250W?
  11. R

    Spot the mistakes - Billy Bulls**t circuit sheets i think

    I went to look at a hotel today, the first thing is the old boards which have various gaps and 3Ka breakers JB's everywhere, and look at the recorded results !!
  12. A

    Very high prospective fault currents.

    Ze 0.02 giving a PEFC reading of 12.4kA which equates correctly; high but acceptable with fitted 100A BS 1361 supply fuse. However, PSC reading of >50kA. Instrument (Fluke1653B) checks out ok. Any ideas? Will be contacting supplier when I discover who the supply company is.
  13. A

    Why is Zs higher than Ze+R1+R2?

    I've had 2 instances in the last week where the Zs measured result was higher than I would have expected. Firstly, a brand new shower feed, R1+R2 of .11ohms, *Ze (measured) of .31. I would expect a measured Zs of between .35 and .45 for this, yet it was .55ohms. Then yesterday, connected a new...
  14. D

    higher voltage needed

    Just received a new lab oven that calls for 415V 60HZ 3 phase @ 45KW, the problem is that we only have 120/208Y available to us ( plenty of unused service). Question: Do I source a transformer or look into converting oven to run on 80A 208y?
  15. Energetic

    Inverter showing higher kWh than the meter...

    Any ideas? Inverter showing 120kwh and meter showing 103.
  16. D

    Phase continuity resistance is alot higher than neutral resistance

    whilst testing a new build i have wired the phase to phase continuity on a ring main, the resistance was 1.88 and the neutral was .51 . ive taken off every socket and checked all connections but still have the same reading. any suggestions?
  17. C

    EU electrical safety standard higher than UK standard.

    I was asked by a client to put up a couple of Chrome bathroom wall fittings, bought from John Lewis. There was no earth terminal, only live and neutral. I rang JL and was told, that most bathroom lights, had no earth, as the cables were double insulated. Yet the shell of the fitting is metal. I...
  18. B

    Zs reading across RCD

    Hi all with a heathy ZE ..22 on a TN-s system i had a R1+R2 of .40 oh my suprise to find that the Zs was 1.01at the furthest socketrechecked my ZE.22?? rechecked ZE from out going terminals of RCD .60 has any one else found this ps i realise that this reading is fine as RCD protected just...
  19. R

    Zs readings slightly higher than ze+r1+r2

    Hi, This is my first post and hope someone can help. I have tested a TN-S system and have these readings, I am constantly getting a higher Zs than the Ze+R1+R2. The Zs is about 0.01 to 0.04 higher than my Ze+R1+R2 readings. My Ze is 0.14 and PFC 2.1KA. I have zero'd all 3 leads...
  20. P

    Higher learning and HNC

    Alright fella's At the moment i work for HMRC and am about to start my 3rd and final year doing the 2391 course. Hopefully after that register to a competent scheme and start getting some work and build up my experience. My teacher said last year i should do the HNC course in electrical...