insulation resistance | Page 2

insulation resistance

  1. B

    UK Insulation resistance whole board.

    Hi all. Changing a CU in an ex-council flat, pme system, no RCD's, and initially tried to IR test whole board L/N joined to earth, got a reading of 0.28 Ohms. Then did each circuit individually (2 X RFC, 2 X lights, 1 X cooker), L/N joined to the circuit's CPC, and got between 0.25 and 0.30...
  2. KeenPensioner

    Insulation Resistance zero Ohms

    Hi all. As I've said before, I'm not an electrician but an adult learner. I have a second hand Fluke 1653B MFT which is out of calibration but I use a CalCard to see how far out it is and it's not too bad. I've watched a thousand videos on EICRs etc and just want to increase my knowledge - if...
  3. timhoward

    Insulation resistance difference both ends of ring final cct

    Initial fault was RCD tripping, narrowed down to a ring final cct. IR tests on that cct with all loads removed were showing almost zero between neutral and cpc. So I broke the ring apart and eventually found the nail through a cable, and got that all sorted. Now its testing ok in as much as...
  4. J

    Insulation Resistance query

    When doing domestic testing, I spend quite a bit of time removing loads & vulnerable equipment prior to carrying out IR tests- allowing me to test between L - N without risk to vulnerable equipment or getting inaccurate readings. I’ve spoken to a number of sparks who go straight to testing L&N...
  5. K

    Low Insulation resistance test on smoke detectors

    Hi Everyone Just a question bothering me as you cannot do Insulation resistance test on smoke detectors as they can become damaged so obviously smoke detectors are sensitive but they are also installed on lighting circuit so if perform low insulation resistance test 250V between Live and...
  6. D

    Insulation Resistance - Low Reading on Ring

    Newbie Testing Question: I am getting a very low IR reading between L&N on a kitchen ring (0.01M). The ring was working fine with no tripping before testing. Can anyone shed any light on what may be causing this low reading? Thanks
  7. J

    Insulation resistance on new installation

    I have recently completed a rewire as part of a complete back to brick renovation in a pretty standard domestic property. Upon carrying out initial verification I uncovered a few strange IR readings. Multiple circuits with low(ish) readings of around 150-200Mohm. However they all tended to rise...
  8. D

    Is it ok to do insulation resistance test on RCBO at 500v?

    I know you are not supposed to do a insulation test on circuits that are protected by an RCD at 500v because it may damage the electronic components inside the RCD so that's why you switch the RCD off before you test the individual circuits, however, what if the circuits are all protected by...
  9. Q

    Insulation resistance query old style hager rcbos

    When carrying out insulation resistance testing on old style rcbos (hager) I understand you are supposed to disconnect both line and neutral aswell as both the neutral and functional earth fly leads.....however does this in theory mean you need to disconnect the above for all rcbos at the same...
  10. S

    Low insulation resistance and tripping circuit breaker

    I've just done an insulation resistance test between line and earth and got 0.0 Mohms for most circuits. Obviously this is an F1, but what I don't understand is why the CB doesn't trip. Is the answer that the resolution on my tester isn't high enough? So I could for example have 0.049Mohms and...
  11. J

    Insulation resistance on modern installations

    On initial verification of new installations I have been having a hard time with insulation resistance. With RCBOs, fixed LED luminaires, intelligent dimmer controls and other sensitive equipment now the norm on almost all installations how do we overcome this and still carry out effective and...
  12. D

    UK Low Insulation Resistance Test

    Hi guys, Hoping someone can clarify some things here. I had a socket replaced in my kitchen recently and as part of this, the electricians did an Insulation Resistance test and told me the reading was very low at just over 1 mega ohms. They advised me to basically rewire the ring (at...
  13. mak

    Insulation resistance test on a ring final circuit

    Might be trivial question. My understanding is that we test on either leg of the ring since both legs make up a radial, but some say they test both legs at once, i.e. LL to NN, it would make sense if the other leg is not insulated since this is a live test, but I don't see why not if the other...
  14. B

    What are the possible causes of low IR readings at 500VDC?

    Kitchen RFC 2.5 T+E - IR=>200MOhms at 250VDC L&N to E but 0.34MOhms at 500VDC L&N to E. I suspect damp/corrosion in sockets, what do you reckon? All socket switches opened including SFCU to cooker hood, F/F, D/W and W/M.
  15. wsoppitt

    Insulation resistance issue.

    This is a new 1 on me. Testing a ring final circuit within a timber outbuilding. All clear on insulation resistance with socket fronts connected but not screwed into metal back box lug. As soon as I connect any of the plates to the back box I'm getting around 16megohm between n and cpc. When...
  16. E

    Insulation resistance check on LED fittings

    Hi, Do I need to disconnect LED fluorescent fittings when doing an insulation resistance check? Thanks
  17. M

    What are the implications of a failed Neutral - Earth insulation resistance test?

    Greetings! Newbie here! We have 3 phase installation in our Lighting dimmer rack. During Insulation Resistance testing on Earth-Nuetral, readings was 0.33Mohm on 500v test. What causede the failed test and how can I troubleshoot? Thank you! Markus
  18. B

    Insulation Resistance Calculation

    Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the working out myself and came up with the same answer as him, so either the paper is wrong or something has literally left my mind!! "Determine the...
  19. G

    Insulation Resistance Testing

    Should I remove all the loads when testing between live and neutral?
  20. Q

    Insulation resistance with vulnerable equipment unable to be removed

    Good evening Was wondering when testing for.insulation resistance and there is vulnerable equipment in circuit but unable to disconnect, I understand that you combine the line and neutral conductors and test to earth. I am just wondering if it's ok and safe to do this at 500v as there is no...