isolator

  1. F

    32A commando socket without isolator

    Any issues with installing one of these without an isolator? The D.B is about 3 meters away and the commando socket will be mounted under a kitchen worktop for a coffee machine and there isn't enough room for an isolator.
  2. S

    16mm SWA tails maybe 9 mtrs from isolator on a 100a supply, and other concerns - EICR opinions

    This has come up many times before and after a couple of hours reading previous posts I'm no closer to deciding on a code, note or nothing at all. BS7671 allows 16mm tails on 100A fuse if demand is less than the cables CCC, I have 16mm at 94amps and the max demand is 60a. From a previous post...
  3. J

    Is a Fan isolator required

    Hi guys you've likely had this asked a lot on here. I have been asked to fit a extract fan wi timer in a bathroom for a friend, i have told him he should get a fan isolator but is adamant he does not want one for some reason (for all it would cost). Is it still ok and safe for it to come on with...
  4. R

    Bno Supply - Isolator

    Hi, I am quoting the switchgear for a BNO install. I have only worked on MEM (Glasgow) isolators but was looking at the contactum TPN 200amp isolator as another option. I need some advice, if I should stick with the MEM. I will be terminating 95mm in the isolator after the UKPN cutout.
  5. Andy78

    Isolator when inverter is remote from consumer unit

    I have never done PV but a customer has had a system installed and has a few issues with it, most of which are being sorted out. I have a question, should an isolator be positioned next to the CU when the inverter is in the loft ? I have never seen one without, and had advice from other...
  6. R

    Fan isolator in separate room.

    Been to look at job today to wire lights and a fan in three separate shower cubicles on a campsite. Each of the cubicles will have a separate internal shower enclosure, toilet and hand basin. The lights/fan will be controlled by pir which activates as someone enters the room. I want to fit...
  7. A

    Rotary Isolator that takes 2x16mm?

    Does anyone know of a rotary islotaor, weatherproof, that'll take 2 x 16mm incomers? I've got long runs out to parking bollards so they've had to size up the cable for volt drop. I could do it with a street light cutout but it wouldn't allow them easily isolate it. Many thanks for any help.
  8. jaydub

    100A DP Isolator Installation Between Meter and CU

    Hi guys, When installing a new CU does anyone ever install a 100A double pole isolator switch between the meter and the consumer unit? Very often I come across 16mm tails which need to be upgraded to 25mm so I join the old tails to new in a Henley block and get the DNO to come and upgrade...
  9. S

    Extend lighting circuit from fan isolator?

    Installing emergency stairwell lighting in an HMO. Is there any reason why I shouldn't start off from the fan isolator (live side obviously).?
  10. G

    Fan isolator switch access

    I have attached a photo of an isolator switch which is for an extraction fan in my kitchen. The only way I have found to switch it off is to take the front plate off which then gives acces to the switch. Is there a key/tool that can be used to turn the switch off/on through the slot in the front...
  11. M

    Need help with wiring a fan isolater, testing unit possibly broken.

    Hi, I had a problem with the fan isolator in the bathroom and it cut out. So I had a look at the switch and replaced it. But that didn't fix the issue and I am wondering if the unit itself has gone. Is there a way that I could test it? This is how the switch was wired. And this is...
  12. J

    Getting an Isolator fitted - With pics....

    Hi Folks, First time post here..... I'm about to start upgrading my kitchen - and I've got a few bits of wiring to sort. No big issue, but the main thing that needs doing is the backboard for the consumer unit needs changing. Reason being - there used to be an electric storage heating system...
  13. W

    Isolator switches ???? Neon

    Hello Is a double pole switch with a neon okay for functional switching e.g as a light switch. I’m just curious .
  14. P

    Isolator for 63A chiller?

    Ay up lads I'm about to install 10mm2 5 core swa for 63 amp chiller protected by 63a MCCB, should I provide rotary isolator for it? Chiller must be working 24h/7 Its my first industrial install and probably my pay rise depend on it. I know there is the reg saying "means of isolation shall be...
  15. I

    seperate light circuit not going through main isolator on control panel

    Hi just wondered if someone could clarify the regs for me,got a control panel feeding a machine isolated by a three phase isolator which also turns the lighting off ,but we need the lighting to remain on when the isolator is switched off,what are the current regs regarding this thanks
  16. Msitekkie

    Bad experience having isolator switch fitted by Scottish Power/Actavo

    I "recently" contacted my DNO to have an isolator switch fitted beside my meter (my consumer unit needs changing and I didn't want to pull the fuse). I was told I needed to contact Scottish Power who charged me £85 but failed to turn up for the appointment, resulting in me having to contact them...
  17. D

    Fan Isolator switch alternative

    Hi. Random question, but in our utility room we have an extraction fan like what is normally found in a bathroom. Currently doesn't come on with the light or anything like the bathroom one. It has its own independent isolator switch which leaves the fan on or off continuously. Does this have to...
  18. joel89

    3 phase Isolator in series

    hi all I am fitting a rotatory isolator in series with the panel door mounted isolator on a star delta radiac saw. The current main isolator located near the DB has Red, Yellow, Blue coming in. Going out on Brown across red Grey across yellow and black across blue. The cable goes to the panel...
  19. K

    Query - Distribution Board to Isolator

    Hello! Im an AC/Fridge Engineer just gone Sole Trader. So Im trying to price up an AC install package for Domestic and Commercial Customers and im scratching my head when in comes to the cost of wiring some Twin & Earth from the Distribution Board to an Isolator on the Outdoor unit. First of...
  20. R

    Isolator versus protection device on main incomer

    Hi, i'm only a student so please forgive me for the basic question: Say you have a generator or power transformer serving a main mccb panel, why can't the main switch of the panel be just an isolator? I've only seen the main switching device as a mccb or acb. I know that in a house you'll have a...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

TrueNAS JBOD Storage Server

Back
Top