I've noticed at my grandparents house that all the MCB's in the consumer unit are all type C, every single one of them. Including the ring final circuits and lighting (there's no fluorescent lights in the house at all). The house isn't that old as well. Maybe about 16 years old. With me being a...
My Neff double oven is tripping the MCB on the mains.
This occurs when I switch on any function of the top oven. The model is U1744N (around 15 years old). The top oven has a double element at the top (grill and oven) with a second element under the casing at the bottom of the top oven. The...
Hello,
I am currently working on a project that previously utilises a charger for a battery system that is connected via single phase 240V AC mains. The existing charger has the 15A inlet running through a 1P 16A schneider MCB with the active line connected to the MCB (with earth and neutral...
Was called out to a car park where they had the lighting circuit tripping out. Fixed the issue by putting damaged cables in an IP rated box. However just realised that the electrician who came out before myself took out the RCBO and replaced it with an MCB in hope that it would stop tripping...
Hi everyone,
I've come here as a DIYer asking for professional advice/opinion.
I have an 8.5KW shower on a 6mm cable and a 40amp MCB.
The shower works fine........for about 8 minutes! It invariably trips out. Sometimes it lasts 6 minutes, sometimes it lasts 10. I was considering changing the...
Good evening
A cable was loose in a ceiling void causing a short circuit this didn't trip the 10 amp 6ka type b mcb but tripped the 50 amp type b 6ka mcb that supplied that board back at the mains.
I am wondering why this occurred other than me thinking the local protection isn't very...
I have isolated the MCB feeding my garage when switched on trips the RCD. There is no load on the garage I have an internal switch in the garage that switches all circuits off. So the fault must be between the MCB and the garage switch. The armoured cable is under the patch so to dig up would be...
HAD AN ISSIUE WERE THE MCB WAS TRIPPING WHEN TRYING TO OBTAIN ZS READING TESTED METER ON OTHER CIRCUTS ALL OK TRIED DIFFERENT TESTER STILL TRIPPING MCB WHEN CARRYING OUT TEST CIRCUT IS ON AND ALL HEALTHY WITH MARTINDALE PLUG IN TESTER GOING TO SWAP MCD OVER IN MORNING ANYONE HAD SIMILAR
Not sure if this is possible but just putting it out there...
Current Situation
Need to tidy up some of the mess in the garage from the previous owner of the house. Wires going all over the place.
Additionally, all of the upstairs lights, the garage light and an external light are all radial...
Hello,
Could you please help me, I would need to install Triton T40i Bath/Shower Mixer Booster Pump, this is a "booster shower" only and not an "electrical shower" whose specifications are as follows:
Electrical Voltage: 240V Pump motor rating:73 Watt (nominal) Water Inlet connection ½” BSP...
Advice needed! Ive been to see a job for garage power, the previous electrician has taken a 4mm on a 32amp B MCB protected by a 30mA RCD. But hasnt done anything with, apart from the fact there is no protection and its T&E all straight forward. My ownly question is do i gland straight into a...
Hello,
We live in an old stone built ground floor flat, built in the 1880s. Obviously the consumer unit and cabling has been updated a number of times over the years by previous owners. One being the Local Authority who owned the property back in the 1960s -70s.
We have lived here for 25 years...
Is there an over the counter device for this?
Is it something that is done outside of a lab?
Been asked a few times, how do you know it'll trip.
Or when forced to use second hand MCBs it would be nice to check them.
Can a 2kw (on a 1.5mm manufacturers flex) fitted oven and a 6kw hob (on a 2.5mm manufacturer's flex) be connected into a cooker outlet plate behind the cooker? The circuit is wired in 6mm t&e on B32 mcb. It has a 45A cooker switch with 13A socket in the kitchen (within a metre of the appliances)
DIY expert tried changing his own Consumer unit from an old 3036 re-wireable CU to a 18th Edition (100A main switch / 63A 30mA RCD / 7x MCBs) I was called out because he couldn't get his sockets (ring main) back on - NEITHER CAN I, I HAVE TRIED EVERYTHING I THINK...
The Lines are terminated...
Hi all,
I’m hoping someone will be able to give me some advice on my oven. Tonight I had both ovens on (as has been done on several occasions). When I went into the kitchen about 10 minutes later I noticed the oven was off and had tripped the 32Amp MCB.
I reset it at the CU and it came back on...
Evening everybody,
I’m wondering if someone wouldn’t mind answering a question for me about RCDs.
I had a water pipe burst behind my washing machine this evening, and once I’d isolated the leak I noticed the sockets had tripped. When I went to reset the breaker, I noticed that it was the RCD...
Does an MCB protect against fault current in the same way as an RCD does? As in, both devices trip by way of detecting imbalance in the Line conductors and thus using magnetism to sprag the switch?
I ask, because if so, I can’t get my head round why an RCD is better than an MCB. I know that it...
Hello, I have tried to search the forum but have not found anything although this must have been asked a thousand times.
When completing a board change for example and there is no end to end on the neutral does downgrading the mcb to a 20amp and effectively running two radials from the same MCB...