micc | Page 3

micc

  1. M

    Micc

    Hi guys any idea what 100m drums of 2L1.5 pyro would fetch for scrap? Don't really fancy taking a drum down to find out.
  2. M

    6 x 100m drums 2L 1.5 MICC FOR SALE

    I have 6 drums of 2L1.5 for sale unused from a job. Have been stored in a dry unit. I have 4 Orange and 2 Red drums.
  3. G

    Micc cable max load

    Hi all can anyone help I'm working on a 3 bed bungalow the incoming supply is pme'd in a garage over 30 meters away from the property and the ccu is in the house which is being fed by a 4 mm micc/pyro from the garage. What is the max load for this type cable thanks mike
  4. C

    MICC advise needed

    Hi All I am in the processing of testing a house ready for a new C.U , all circuits check out ok but there is a plastic coated micc feeding a shed in the garden which is glanded onto the top of the original metal rewirable fuse board. I have to extend all original cables to reach the new cu (...
  5. B

    IR testing MICC

    Hi all my problem is when IR testing MICC the readings keep droping to 00M ohms:sad_smile: i have 29 circuits to test in a large building, and the circuits i have so far tested have all been 00M Ohms ? could any one offer me some advice please. Bare 2L 1.5mm MICC. Any other problems i might...
  6. ringer

    Olives for MICC glands

    Is it possible to buy just the olives used in MICC glands? Had to cut back some pyro this week to remake the termination, was unable to salvage/reuse the olive, and ended up having to buy a whole new gland. I know that glands are not terribly expensive, but all I needed was a new olive (and pot).
  7. ringer

    EICR in Church - Low IR in MICC heater circuits

    Recently done a EICR in a church and about half of the heater circuits (tubular heaters fed by MICC routed under the floor) had low IR, typically 0.18 to 0.61 Mohms. There is a lot of damp in the floors, and I have to explain to the customer why the circuits are failing the tests so that they...
  8. N

    Micc

    Hi guys I've a small pyro job coming up and I haven't done any since my apprenticeship(a long time ago).I have been searching you tube looking for a video with no success.Anyone know of any online. I'm sure I'll be ok with it just a kind of refresher. Cheers
  9. D

    Advice on alterations to MICC please

    Hi all, Just been to look at a job in my brothers shop, all the old wiring is installed in MICC with a metal clad conumer unit, as it once used to be a bank. He is having all the shop refitted, and wants me to move lights about, install new lights and extra sockets e.t.c and points for...
  10. the pict

    Micc

    Today I undone a tangled mess of cables in a enclosure it contained lighting and heating and alarm cables none with any id, after about 3 hours I had the whole lot sorted and reconnected, apart from one MICC which had the conductors exposed taped and silicon sealed as a insulation method, no...
  11. W

    Csa of MICC sheath on a 16mm 2core micc cable

    what is the earthing value (csa) of the sheathing of a 16mm 2 core MICC cable
  12. S

    MICC to meter tails

    Hi all, i have a job i am currently doing in an older building that has 2 x MICC supplies running into it. the old distribution boards were metal so the MICC gland terminated straight into the board housing provided a connection with the earth bar as that too was connected to the board...
  13. W

    clearing fault on micc

    Fault on micc, one leg of two-core down to earth. Anyhow big probs cos fixed / glanded into conduit box in concrete ceiling...supposed to be phased and tested before, the fault magically appeared after! Ideas what to do and get out of hole before boss finds out We settled on one guys idea who...
  14. E

    micc cable in 1960's underflloor heating

    I have split the micc cable leading up to the room stat in my appartment and was wondering if anyone know how this will be wired as i have no wiring diagrams for the installation. I am an electrician but have no idea how this is connected. I know that its fed from economy seven on its own board...
  15. K

    Church Installation PVC? SWA? MICC? Mixed answers.

    Hi there i have a job to rewire part of a church and the original is wired in pvc just wanted to no what the trend is? thanks kinger.
  16. sythai

    MICC rip out.....

    Morning chaps... We've got a rip out today and will have a fair bit of MICC. Just wondering if anyone has taken it to the scrapy's before, wondering how they will class it ? (shame it's been painted) Cheers, Sy
  17. G

    MICC (Pyro) Sheath, Actual CSA Sizes.

    Physical cross sectional area of MICC/PYRO copper sheath when used as CPC. 2L1 ****** 5.4 mm2 3L1 ****** 6.7mm2 2L1.5 ****** 6.3 mm2 3L1.5 ****** 7.8 mm2 4L1.5 ****** 9.1 mm2 2H1.5 ****** 11 mm2 3H1.5 ****** 12 mm2 4H1.5 ****** 14 mm2 2L2.5 ****** 8.2 mm2 3L2.5 ****** 9.5 mm2...
  18. S

    MICC Cable Outer Sheath

    Hello, Under the 17th Edition are you still allowed to use the outer sheath as earth ?
  19. S

    MICC cable strightener for sale...

    £20 inc p+p! cheers
  20. S

    1.5mm MICC as a ring ?

    Hello, Can somebody please confirm I'm not going crazy. I'm about to change over the CU at my flat as part of my Part P appraisal, and I've discovered one of the rings is wired in 1.5mm MICC. Looking at the at the current carrying capacity: 1.5mm MICC / Ref method C (embedded) = 28...