I've got a lighting circuit with no CPC. I'm telling them they have to go all plastic, There are also a good few 240V downlights in the kitchen though. What can be done with them???
Cheers for any help.
I have carried out a PIR on a domestic property which has an old Wylex rewirable fuses and there is no cpc to the lighting circuits which I have recommended improvement. The question is if they just want the DB upgrading is it possible to leave the lighting with a note on the EIC? All wiring is PVC.
Posted a few weeks with regards to eicr, only one cpc at ccu on rfc, went back for remedial works yesterday, the ccu was removed and cables pulled up to see if there was another cpc there as were two lines & two neutrals at ccu but only one cpc. we found that the rings were installed in singles...
I'm carrying out an EICR on a ex-council property. It's a low rise block with metal cabinets and an old 70's wylex CU.
few issues:
Single core cabling throughout.
There is no cpc on the lighting circuit. No cpc's on the metal backboxes on the plastic switches. All the pendants are plastic...
I've just installed a couple of additional 12v down lights and changed extractor fan in a bathroom. The lighting circuit is one with no CPC.
How would you complete a MEW?
Obviously tests are limited in this case, but where would you use LIM, X, - etc in the relevant boxes?
thanks.
Hi all,
Had a call from a customer saying her oven had broken. When the oven engineer went out he fixed the oven but told her she had "no earth on her kitchen sockets".?!?! He told her the other circuits ie the lounge and cooker, were ok but no earth to the kitchen ring final?! How can this be...
Hi sparks.
Little question. Have just done a EICR on a old domestic installation. T-N-SC. No cpc in the lighting. Wylex Rewirable fuses. 30mA RCD installed before the board. This is has failed the trip tests. What do you suggest I recommend? Do the lights need rewiring or will a new RCD/board...
Hi,
I have just tested a RFC and the CPC was broken (no continuity). Tested all the socket on that circuits and R1+R2 was OK but I could't open a socket to check, as it was hidden (burried) behind a door frame and it must be a double socket with only one of its switches staring at me. To reach...
hi all
i was wondering how you all felt about doing pt&i on older houses...rented..
i have been asked to do 3 for a landlord customer and although they have passed a test i still have concerns about the installs.
i guess what im saying is i have a feeling that if i really look hard (which is...
hi guys, anyone got any views on this, got asked to price up a 16Amp solar pv circuit with DP 30mA RCD, (invertor etc by seperate company), c/u is already 17th edition and PEB to regs, but the 2 lighting circuits don't have any cpc.(thought 17th c/u could only go in to replace a disstressed c/u...
Probably going over old ground here but I have assessment soon on this job, new consumer unit fitted completed R1+R2 test at light pendants all ok but two way light was found to have no cpc at light switches although does have earth at pendant what can i do for my assessment have read esc...
I was asked to change a light fitting for a friend and replacing the old plastic pendant from a metal class I fitting but there is No cpc.
Without ripping out laminate flooring ect there is no no way i can get a cpc from the downstairs circuit, which this light is on.
The Upstairs circuit has...
All,
Looking for opinions please:
Just been to see a client who has had another sparky in who has connected up an outbuilding which has a number of 2 gang sockets and lights - all from a 13A spur off the ring - no RCD protection anywhere. He was due to change the CU but has said he won't...
Looking at a CU change for a young couple with kids.
There is no CPC on the lighting circuits, the cable is 2 core (red and black)
I have done a IR and continunity and all is ok, no borrowed neutrals
All the accessories are Class 2
The young couple don't have the budget to have the lighting...
was asked by a friend to put up some light fittings for his mum, changing from pendant to some fancy metal fittings, discover that there is no cpc on the circuit.
Running a cpc or redoing the whole circuit again from the CU is going to be difficult, newly decorated pace all laminate flooring in...
Found out the hard way on a job today the lighting circuit for the whole house has no CPC.
I understand its ok aslong as all light fittings and switches are class II, RCD protected, sticker on DB etc.. but what about the pins on switch plates? surely if the backbox were to become live so would...
hi - just changed some light fittings for a customer, tested and found no continuity from phase to earth. checked the CU - (earth present) and found a box above it containing 2 core and earth choc blocked to 2 core no earth. presumably when the last CU change (looks like eighties) they simply...
Hi all, just took a small job on doing some alterations to a kitchen and adding some spot lights. As a separate job I will be installing a new CU.
After a quick check of the exsisting lightig circuit confrimed there was no cpc, I strongly advised the customers that they should, at the very...
Folks,
Doing a bathroom job presently and none of the lighting circuits have a CPC....it's an old topic I know and I'm aware of of requirements so I'll not be fitting that fancy bathroom spotlight!
However, what in theory is wrong with *temporarily* borrowing a CPC from the adjacent...