Hi. please advice on the following. My generator is Stamford /Newage 125 KVA, 415/240 Volts, 174 Amps, 1500 rpm, pf 0.8. I want to build a load bank comprising heating elements each of which is rated at 6 Amps. I have a total of 36 such elements. I have divided them into three groups. My...
Was reading my OSG earlier and was suprised to see it recomends a 32amp circuit for a cooker up to 15kw.
Also says you can have multiple cookers on one circuit/isolator (which I knew)
My question is this
Can I have a 7.2kw hob through an iso on a 6mm 32a circuit then on the other side of the...
I've been asked to run in a supply for 2 2.8kW fan assisted ovens (none of them have hobs) but there is only 1 spare way on the main board, if it was only 1 oven 2.5mm would be big enough as well as a 20A fuse but as I need to supply 2 using 1 MCB I'm a bit weary as to how to do this safely...
I'm after a bit of guidance here! Being an old fashioned type of chap I always ask what size oven is being installed to get the calcs right, however I recently carried out a Periodic on a property to be let and found that the oven was fitted with a 13A plug and plugged into to the kitchen ring...
My parents are having a new kitchen installed soon and had someone out today to check over the room before they make their final decisions.
My mum wants a double electric oven and induction hob, but the kitchen fitter has said that the cable installed (which is completely hidden and...
hi guys.
right i'm doing a kitchen next week and the customer has got 2 ovens (both 3.8kW) and a induction hob (10.8kW).
The hob will be on its own circuit with a 10mm T&E supply.
As for the 2 ovens. I have the possibilty to supply both of these with a 6mm T&E but all they need is a 20A DP...
Hi Guys
A Happy, Healthy and Prosperous New Year to all of you.
Let the battle resume!
Customer has changed his mind. I was supplying a built in Double oven off a 6mmsq 32Amp protected radial and a built in microwave off a 13 Amp spur on the ring.
He now has two identical self cleaning ovens...
If a customer has 4mm t/e run from 32a mcb to oven switch with socket.
From there it runs to a FCU behind the oven and fused at 13A.
Cable is in plaster from ccu to ceiling then accross kitchen in ceiling void (no insulation) and back down wall in plaster again.
First question - Is it correct to...
Hi All,
We have an hotpoint electrical fan oven, that is tripping the fuse box when it gets over 160 degrees, it should be able to get over 200 degrees.
I thought it may be the thermostat, but why would that cut the power to the fuse box, has anyone got any tips on what to look at first...
im doing a job in a kitchen this week that as no existing cooker radial my question is
can i run two ovens rated at 3.650 and 1.900 on the same 6mm cable
if so would these need two separate 45amp cooker switches fitting
and also should i take diversity into account and im also a bit...
Have read on this forum several times from experienced posters that ovens rated at 2kW must have their own circuit. However, was chatting at college to a guy who teaches some of the regs evening classes and he said that a small oven below 13A could be on a ring. :confused: Anyone shed any light...
hi everyone,
i went back to a job that i previously changed a consumer unit and certified. and i have noticed the builders/kitchen fitters have attached two 3.5kw ovens to a 32amp mcb 3 socket ring circuit wired in 2.5mm twin and earth. i have told the client. what else can i do? help grately...