I've been asked to install a shower unit in a clients house and he only wants me to change the shower itself. The consumer unit has BS3036 rewireable fuses and no RCD protecting any of the circuits, including the existing shower circuit. He has already bought the new shower and only wants me to...
Hi everyone.
I'm after abit of help calculating cables sizes and protective devices for a 3 phase DOL motor.
I haven't worked on 3 phase equipment for many years and 3 phase calculations is as far back as college so please excuse my ignorance on the subject and not knowing answers to perhaps...
OK, going to keep this short.
Supply is 150mm 4 core SWA, with NO supplymentary earth ( calcs done by others, )
QUESTION IS. Do you NEED to run an earth ( is it a regulation) from banjo on inside to earthing terminal inside board. Common sense and a simple ohms continuity test (0.01 ohms)...
Bit nervous about putting this on the open board, normally stick to the trainee section.
Hope i can get some help. I have recently qualified so dont be to harsh if im not 100% correct.
Ive been asked to help an older spark to pull a a 3 phase SWA cable. Ive been asked to design the circuit...
Hi Folks,
I am filling out a minor works certificate for 2 fused spurs I have fitted from 2 socket in the livin room to supply 2 wall lights 5A fuse fitted in spur.
My question is on the minor works cert where it says Method of fault protection, do I put Automatic disconnection of supply...
Hi just checking the main protective bonding conductor size on a tns system, there are two supplys the tails sizes are both (630x2 the supply earth is 240 and neutral is 630x1) persupply
designer aspecified main erthing conductorto met fothe main protective bonding as 2 x 240 i think this i...
Was asked today why we can use the armouring of an SWA as an Earthing conductor but not as a main protective bonding conductor unless we apply the resistivity formula for steel which result is8x that of copper. Can anybody explain this in simple terms because the person i am trying to explain...
A circuit wired in 6.0/2.5 with a 32amp MCB feeding a double socket for a gas hob and gas oven.
Now I know that the protective device is for the cable, but I am concerned that the socket can only take 13+7. Should I down rate the protective device for the socket and not the cable in this...
Hello all..
I have been asked by a customer to fit a recessed socket in the kitchen. The socket will be located on the side of a cupboard (no other viable options). I have given them options of nice looking wooden surface boxes but they are adamant they want it recessed.
I want to cover the...
There's hundreds and hundreds of different protective devices around that you're likely to come across sooner or later. They all operate slightly differently and they may appear different in shape and size but they've all got one thing in common in that they will facilitate the disconnection of...
Hi i wanted to clarify what 7671 says about wiring of outdoor lights.
presume the job is a lamp post 0.5M away from the house. Fed from a fused spur unit, with a downrated fuse, inside the house from the upstairs S/O ringmain. The cable would be 1.5mm2 twin earth from the fused unit wall...
Hi, testing a UNI with one main supply, which in turn feeds around 10 separate building. Each building as it own Gas supply with meter, so therefore a Protective Bonding Conductor to each incoming supply. Does the size of the cable have to correspond to the incoming supply size, or to the size...
I'm doing an continuity test on a lighting circuit and I'm getting funny readings I'm putting on test lead on earth and one on switch live then I'm getting a reading of around 1.4 ohms but then when I'm checking the polarity it's shooting up to around 93 ohms but not breaking the circuit as you...
B. Gas decided to a. relocate a customers meter and b. connect it to the gas main in plastic. The old meter was removed leaving a stub of pipe with the MPBC still connected. My view is that this is now an earth rod, auxiliary to the distributor earthing conductor.. Another guy looked at it and...
Hi all.
Could someone with better understanding help clear this up for me please;
In the Regs (544) there appears to be no value of resistance for the above and also states that if copper, need not exceed csa of 25mm2.
In GN3 it talks about using a value of 0.05 ohms for verification of bonding...
Hi I am working in a hotel and I found that a 3-phase DB was fed by 2 seperate swa cables one containing the 3 phases and the other a seperate neutral and earth I know this is bad practice but can someone tell me why the NIC firm have picked this ad a fault I would not have done this myself it...
Hi all,
I have been asked to bond the gas and water of my neighbours house as British Gas have picked it up as not bonded.
The consumer unit is an old Wylex one with re-wireable fuses. Ideally needs replacing with MCBs and RCD protection but they are not willing to do that until next year...
Hi all need some help,
I was called to a job to do some rectification work after a so called sparkey half wired a house.
He decided to run a 10mm T+E from a Henley block located in a cellar to a second C/U three floors up, I'm going to have to change the 10mm to 16mm.
My question is what do I...