    UK I am getting very high zs readings

    Hi Guys. When measuring zs I get very high reading. Ze is 0.3 (tns), zdb is 0.21. r1 and rn are is 0.42. r2 is 0.72 , r1+ r2 is 0.29 . when I test zs it 8.26 ohm new to testing. I even buypassed rcbo but it stays same. Do you think my mft if faulty? Any thoughts guys? I am new to testing.
  2. T

    Battery/solar/inverter system gives inaccurate power readings

    Hi, I have purchased a battery/inverter/solar system for my home. I also have a smart meter, and an app which links into my smart meter to get the power data from the smart meter. The battery/solar/inverter system also tells me how much energy I am using. However, its readings are not accurate...
  3. P

    Low IR test readings on lighting and RFC.

    Hi,guys went to do an EICR and when doing IR test I got L-E ON RFC like 0.02 MOHM and two lighting circuits L-E AND L-N the results were like 0,14 and 0,15 MOHM.It is old wiring where all the cables live and neutrals are black put in the walls in steel conduit.My question is is it possible that...
  4. S

    Voltage readings

    Came across a weird one today… Four single black stranded 12gaTHHN running through 1/2” conduit about 40’ to first outlet box and 70’ to the last, on a branch from main panel. One 20A breaker and one 30A breaker. The homeowner asked to eliminate existing locations and reroute, no problem. I...
  5. Dartlec

    Low Zs readings on MFT1771

    My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a calcard and check it monthly(ish) and keep records, which my NICEIC assessor has been quite happy with for years... I have an original MFT1552 which...
  6. D

    Ring circuit readings

    Hi all I am about 2 years retired after being NICEIC registered for over 20 years. An old customer just a little concerned about an EICR just been done on her property by someone else now with lots of N/A everywhere main one being no end to end readings (R1R2) entered for the ring circuits I...
  7. M

    Does this look like an earthing issue? Meter readings attached

    Hi folks. I am regularly experiencing tingling shocks from my laptop and kettle. Both of these things are plugged into something with a ground plug. I decided to measure the neutral to earth voltage, at least for the nodes I can reach at my plug. I see significant AC voltages measured between...
  8. P

    Insulation readings

    Hi, I’m confused. I recently carried out insulation resistance test on a 3 phase board I had some weird readings. I removed all vulnerable bits of kit and tested the dead side of the incomer all readings where good a part from L2 which had a low reading of 2.8M ohms. This was much lower than...
  9. F

    LOW ZE READINGS

    carrying out an eicr on a building recently we found the external ze reading to be extremely low ie 0.02ohms. so by measurement and testing are fault current read 20ka. now most of the mcbs rcbos ets have an icn of 10kohms. this poses a problem as obvisoluy the mcbs etc would self destruct under...
  10. C

    Martindale et4000 high readings, calibration?

    Hi all I've just purchased the martindale tester second hand from ebay. In comparison with my metrel mi3002 and ht macrotouch, it is giving almost twice the readings. In my mind, this is a faulty unit, as calibrating will only check the tolerance, and if the readings are this far out, it...
  11. B

    What are the possible causes of low IR readings at 500VDC?

    Kitchen RFC 2.5 T+E - IR=>200MOhms at 250VDC L&N to E but 0.34MOhms at 500VDC L&N to E. I suspect damp/corrosion in sockets, what do you reckon? All socket switches opened including SFCU to cooker hood, F/F, D/W and W/M.
  12. S

    High no trip earth loop readings

    Hi, I'm buying a new test kit and was wondering if anyone had a problem with non trip earth loop readings? This was taken on the same installation- new mk sentry split load rccb CU. I've got a secondhand, calibrated megger 1711 MFT which I've taken readings on a ring = 1.04 ohms And...
  13. S

    Question about Power use monitors-inconsistent readings

    Have any of you used appliance power use monitors to measure how much power a device is using? I recently bought one that plugs into a wall socket and then you plug the appliance into the device and it tells you the voltage, amp draw, wattage and Kwh the appliance uses. If I plug a fan heater...
  14. M

    How do i calculate missing resistance readings in a parallel circuit using R1 and Rt

    Hi I am a current student studying to become an electrician and a question has thrown me. I'm wondering if someone could help, there is a question on one of my home work books. "complete the following table assuming the resistors are connected in parallel?" the example I will give is R1 is 120...
  15. B

    Earth readings

    TT system Ze is 17.5 ohms but when connected it is 0.60 ohms? Have one outgoing 95mm SWA and one 240mm SWA earthed either end and individual rods? Thanks
  16. Baddegg

    Bit of damp affecting my readings ?

    IR readings a bit low on kitchen rfc..,..think I found the cause...
  17. Baddegg

    First eicr and low iR readings

    Being new to this game I’ve been waiting a while for the right job to come along and I have now done my first eicr today, small Chinese takeaway 2 circuits (lights and 1 rfc) most cooking appliances are gas, found some interesting stuff like sockets wired from lighting circuit,main bond buried...
  18. cliffed

    Short circuit compliance on high Zs readings

    Would you divide the 5.13 ohms by 4. I personally don’t think so. Also the R1 /Rn short circuit resistances are different from the usual R1 /R2 measurements. Found those in an electrical book by,that man. The Zs on this circuit was above the permitted figure,so just had a play around to see if...
  19. cliffed

    Eicr ring main readings

    Would you guys be happy with these readings on ring main,Rcbo c type 30ma/32 amp. r1 1.87...rn 1.91 cpc 3.20....R1 +R2.1.26. zs 1.46 ohms.
  20. D

    Solar Ammeter readings in/out

    Hi all just registered and looking for an answer to an issue with my installation. I will give you the spec first. Two X BP solar panels each one: Nom peak power 75.00 Peak power voltage 17.00 Peak power current 4.45 Short circuit current 4.75 Open circuit voltage 21.40 Victron energy 75/15...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top