Hello All wondering if anyone could shed some light on a problem i have with my IR readings.
I recently rewired a house.. took care pulling cables in etc . finished 1st fix, checked cables by looping ring main in connector blocks and doing continuity and IR test . continuity was ok, IR read...
Hi all i was wondering if anyone could shed some light on my problem. Came to test a ring circuit today L-L 1.23 ohms N-N 1.23 ohms E-E 1.98 R1+R2 0.73 then i did my insulation resistance tests L-N 500 ohms N-E 500 ohms then L-E 0.00. Nothing plugged in, only a few sockets connected the rest in...
Hi Guy after your best advice, been along to see a customer who is having trouble with his system which has been up and running for just over Four years and the original installers are no longer in business.
He has approx a 17kw system of Schott Asi 105 w panels on the roof Appox 162 info...
Any suggestions on an earth resistance tester which will not break the bank? Anyone got or used one of these UNI-T UT521 Digital Earth Resistance Tester
Sorry just learning but with a short circuit.
V=i x r so dosnt that mean that the maximum short circuit in a circuit with even no resistance would be 230 Amps.
How comes I hear of higher currents in faults and breaking capacity for the breakers are 6ka.
I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the...
Basic question sorry,just isn't coming to me at the moment.
Why can you close the switches foe an insulation resistance test wouldn't that cut off the circuit and not measure the resistance after that switch.
hi all, just looking at upgrading a george ellison old fillled rotary resistance starter on our forging hammer (the starter is pre-war 1924) the contacts are worn and the mechanical lever springs are also worn been temp fixing it for a year or 2 now, the motor is a 3ph 415v slip ring motor (big...
Hi,
I'm after a bit of advice. British gas installing a new boiler, refused to install as fault on electrical system. The RCD trips when performing an ELI test. I've had a quick look tonight, TT system, rcd tests out ok. IR was 10 Mohms on all circuits except downstairs socket where...
Just spotted this on my facebook feed :juggle2: and thought it may be a good exercise for people to have a go at.
What is the total resistance (Rt) of the circuit?
:book::)
Hi, quick question for you all, do u think it is posssible to have an ins res reading of 0.02 on live earth of a lighting circuit which includes em. lighting but neutral earth is above 10 megohms ? There is low voltage track lighting also installed on the circuit.
Also can anyone explain the...
When you do the continuity test on a ring final circuit and you have to connect L1 to N2 and vice versa, this assumes you know which L cable is the incoming or outgoing.
I understand that if you connect L1 to N1 and vice versa the ohm readings rise then fall as you go round the ring circuit...
If when carrying out a "whole instalation" test from L+N to Earth the result is say 50 Megohms, and there are ,say,5 circuits would that mean that ALL the circuits pass the test or do each one still need testing?
I find working as a labourer I never have to think about basic theory, so it's easy for me to forget.
Doing some experimenting tonight with 11meters of 2.5 T&E and a continuity tester.
End to end on the line 0.15ohm CPC 0.20 Ohm
It's not exactly what I expect. Is the difference something to...
Hi,
I am getting a reading of Live to Live = 195 MOhms
Live to Earth = 0.75 MOhms at the distribution board I am working on a Highway depot.
Are these acceptable values?
If not... what do I to?
Thanks,
Lasowski101
Just want to see what other sparks think my nephew who is in his last year was telling me that there tutor was telling them that when your doing 3 phase circuits you use the 1000v range ???????????? Your thoughts please
I'm thinking of buying a combined IR and continuity meter for fault finding on domestic and commercial installations. I'd like something that's smaller, lighter and easier to handle than my Fluke MFT and fairly robust. It would also act as a partial backup in the event that the MFT is out of...
Just finished installing some low voltage downlights to an existing circuit , I'm going to test tomorrow to save disconnecting the lamps/transformers I was going to test LN-E 500v on the insulation resistance test , what do I have to write on the minor works certificate and where to show that...
Hi
I have a earth fault on a customers drive with 30 drive over fittings.
The swa runs past each fitting and has a resin branch joint,with one cable going into fitting.
Have narrowed fault down to cable by dismantling fittings etc.
Is there any tester or method of measuring from the end of cable...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc