Hi guys
Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the Regulation supporting this Code 1/2?
I can see 411.3.1.1 but this relates to Lighting. If anyone could assist Id appreciate it, I know its a fault but...
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in.
Today I was looking at a socket on a final ring circuit. The house was built in the 80s and the socket is almost certainly original to then.
There were 3 cables...
I often conduct EICRs alone. I'm curious if there is a socket tester on the market that can transmit to a handheld unit. The idea was that I could flick switches at the board without running up 4 flights of stairs to check whether it was the right one. Or failing that, a socket tester that makes...
If someone made a request to you, to install a new double socket that would be supplying power to a tumble dryer along a circuit that does not go into a location where those types of device are usually located, like a kitchen or utility room, but goes instead from the hallway into the living...
DIY'er question:
I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The boss lady wants a socket installed there to move the toaster away from where it currently sits, because 'lady reasons'..
Is there any way I can swap...
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this.
I have a double socket, it was on the ring main but due to short leads after decoration the ring was joined behind the socket using 3 way wagos and short leads run to the socket, so it's effectively...
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three green lights came on saying everything was fine and correct. When I took the faceplate off to do my R1 R2s I got readings of 0.60 on R1 but then...
Hi, after some discussion with electricians, does removing a 16A or 32A socket constitute safe isolation? I understand that removing the socket completes an isolation, but for me, additional measures should be included, either placing a lock around the plug to prevent it from being placed back...
Hi,
I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the left isn't doing anything so I was thinking of blanking this off. The reason for moving the socket is I'm building a larder cupboard around the boiler...
Hi, my friend is having a floating shelf with a electric fire, and I’m between minds where to put the socket,
I was gonna put the socket behind the fire which will be fed by a 13A fused spur but I’m having second thoughts about putting a socket behind there due to heat..
Would it be safe...
Hi all. I'm going to replace some sockets during a routine redecoration of our lounge including replacing some singles with doubles with USB charge points. From past experience of doing similar in other rooms a long time ago (certainly before the advent of WAGO connectors), I recall that it was...
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a professional job - I know that. I just want to understand what I should consider so that I don't end up having to rip out or rework stuff afterwards.
The...
Hello,
as a relatively newly qualified electrician (mature trainee who completed his NVQ in 2023) today was the first time I've seen a melted plug. It was at a rental property and the tennant had a fan heater hanging on to what was left of the plug. I'm guessing that the fan heater had been...
Hello All,
I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual current-operated circuit breaker on the supply side (25A, 30mA trip current). The RCD is there because some of the circuits supply power to outbuildings...
Hi All,
We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good standard.
Due to some miscommunication with the electrician however, he forgot to create a separate circuit for the electric cooker.
Looking at the...
Double wall socket switch won't switch off. It just flips back to on. The left side one is fine. It used to do this 3 years ago then was working again. Now it's back. Do I have to replace the entire socket unit? Is that easy to do and legal on your own? Thank you
We are having problems with one socket which my husband has changed the front plate on. When he tried to attach the new front cover it singed the screw and blew the fuse. What could be causing this?
Hello everyone,
We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA, in conduit also. He temporarily fitted a 2 gang socket so we could use power tools whilst we complete a fitout internally, although in that use case...
Hi,
I have a Prima Tumble Dryer which I have had for 5 years.
Just recently, the plug and socket melted. I replaced both and it melted again. I replaced again and again it's getting hot. I measured the temp with a laser thermometer which said it was 42.5oc. I drilled a couple of holes in the...
Hi
Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired into the socket circuit not the lighting circuit (I have never seen this set up before) and hasn’t been fused down. So because of the way the extractor...