Hi everyone
Table A.1 in Guidance Note 3 shows various values of resistance/metre for copper conductors at ambient temperature, including e.g:
18.10 milliohms/metre for one 1mm sq. conductor
0.387 milliohms/metre for one 50mm sq. conductor
But these given values of resistance do not exactly...
If you have a 50A 3 phase MCB, that's 50 per phase - when calculating voltage drop using the tables do you calculate using 50A or 150A?
ie 10mm cable carrying 50A 3 phase over 30m
VD=3.8x50x30 / 1000 = 5.7V
or
VD=3.8x150x30 / 1000 = 17.1V
I think it has to be the first but am a bit mixed...
This is a 2391 question
DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.
45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)...
hello just taken my Am2 exams last week and past everything apart from the 30 question online exam. I have booked myself in for a resit of the questions for next friday.
questions like...
50mm by 50mm metal trunking fixed horizontally over 20m, how many fixings would it need?
that...
I'm working in a new build school kitchen at the moment and am bonding. We have taken earths around all the pipework and fan canopys but what about stainless steel tables, shelving, etc? Would this need to be bonded? Also, tables and racks which are on wheels? Obviously being on wheels you'd...
An electrical control panel, in particular for height-adjustable tables equipped with actuators or lifting columns driven by an electric motor. The panel has a first part (1) intended for fixed mounting of the panel and a second part (2) with operating keys (19) for activate electrical switches...
Hi any thoughts on this ?
Doing a periodioc on a commercial property with a restaurant and kitchen.Lots of metal tables in the kitchen (not fixed) gas ovens,dishwashers etc.
The circuits are rcd protected the main bonding to gas/water is ok
There has been installed a 6.0mm earth cable running...
we have a site where in a school kitchen there is a stainless table with just a sandwich maker on it, we are being told enviro health officer said it wants bonding is this correct? the socket is rcd protected.
Hi all
does anyone know where I could find a table of resistance per meter for he given csa of a cable. I know that, "Robin" produced such a booklet, but as I bought my Robin testers second hand, I didn't get the booklet which saves a lo of calculation.
If not does anyone know where I could...