tails | Page 8

tails

  1. T

    Meter tails through Recessed meter box

    Hi all, what are your thoughts on running new tails from an outdoor recessed meter box,straight through the existing hole into the garage where the CU is situated. Should the hole be enlarged to accommodate some sort or trunking for protection and sealed for fire??? The tails are connected to a...
  2. L

    Feeding 250 amp 3 phase board direct from buzz bar need isolatir

    I'm working in a warehouse and replacing the old fuse boards with a new 3 phase board. The board will be sitting directly above the buzz bar im not sure if I need to put in an isolator in between them to isolate the 3 phase board? Thx
  3. B

    Meter Tails

    Hi. I've recently moved into new house. The meter box and consumer unit are installed in cupboard underneath the stairs, however they are approx. 1.5m apart and the tails are surface mounted. Should they be encased in trunking so as to protect them from damage. Thanks
  4. D

    Meter Tails - Neutral

    Hey guys. Wondering if anyone has came across this before and if it is legal? It is several 1.5mm single cores going into the neutral of the main switch. Main fuse etc is several metres away in communal hallway, but is a 16mm meter tail from there. Cheers
  5. A

    Extending Tails

    I have a job where SEC are moving the mains cable for the property to allow for change of use of the area. This means that the tails from the new meter box will be through a wall and over 3 mts long. Therefore a Switch fuse /isolator will be required in the new meter box. Does it require the...
  6. N

    Meter Tails

    Hi, On site dispute needs sorting. We have a consumer unit 3m away as in distance (not cable length) from DNO (outside meter box, flush with wall). We currently have a 25mm 3 core SWA from DNO to consumer unit. Running within the fabric of building and it's protected from the nails and the like...
  7. P

    Can you earth to ground rod with bigger earth cable than the tails ?

    Quick one. Tails are 10mm. Earthing cable from rod to earthing block inside the CU is 16mm. Where i am, we have the tails in, everything RCB protected and then the earthing cables from the circuits/appliances etc into the earthing block. On my CU, the earthing block is a bank of 'quick...
  8. M

    Upgrading tails

    hi everyone, I am sure this has been discussed many times but what do people think with regards to upgrading the fuse board tails on a consumer unit change? I have one to price up for a flat where the meter cuboard is outside the building, and the tails are run through the hallway up a riser...
  9. S

    Meter Tails hanging loose.

    Been to a job to see this. I'm guessing that when the old CU was replaced the sparks didn't bother to remove the old meter tails - they were live and just had a couple of wraps of insulation tape round them.
  10. Gazthesparky

    AM3 Tails Stuffing gland

    I seem to have a run of jobs of upgrading consumer units. Previously I've used 32mm standard stuffing glands for the tails when I have needed to. Although the sealing gland hasn't got specific holes for the tails i find that it seals well. Anyway I've been looking at the special tails stuffing...
  11. G

    Whiska Quixx

    Just seeing peoples opinions on the whiska Quixx glands for tails? Bad practice to use them without tails clamps within CU?
  12. 1

    help with eicr

    Hi all some advice will be Much appreciated please when filling out a eicr the primary supply conductor would that be the main supply cable coming in to the building or would it be the submain of the board under test in a commercial/industrial installation as going through others eicr and...
  13. B

    EICR meter tails coding

    Morning fellas, Just a quick question if you don't mind, Doing a EICR and came across what looks like 6mm tails from the meter to the rcd, iv never seen tails thats small before, the dno fuse is 60a and its a tt system. What code would you use please, Many thanks :)
  14. Soulsurfer

    Testing issues !

    long story short, Pre-rip out test really old install, TN-S,16mm tails, 6mm main earth ! Ze was 0.22 ohms and 1.2kA fault current. DNO been up this morning to connect new tails 25mm I supplied through switch fuse and 16mm earth. Fit board new, go to check Ze and get 0.00 ohms ! PEFC 10.0kA &...
  15. M

    Supply for shower board

    been to a job today where a seperate fuseboard has been fitted to supply an 8.5kw shower the supply and load cables for this board are 6.0mm twin and earth, the shower fuseboard has a 32a mcb and an rcd main switch and labelled up shower only, the feed for the seperate fuse board (only room for...
  16. HappyHippyDad

    SWA or tails?

    I know I have started another thread in the past with an almost identical title but this one is asking different questions! The DNO are moving the meter box and I will need to extend the tails to approx 8m. The present earthing arrangement is TT, I have asked the DNO to change to TN-C-S and...
  17. N

    ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)

    Hi All, I have my ELECSA assessment in a few weeks time. I was going to install an in-line water heater at a friends house but am now considering a board change at another friends house as this seems to be what they really want to see. I am trying to back up everything I do with regulation...
  18. Soulsurfer

    Hager Cu Number ?

    Hey all has anyone got a code / part number for Hager Design 30 CU 14 way or close to ? I have VML 114 but that's for the Design 10 & can't find any Design 30 boards online for pricing etc... With the clamp for tails etc... Tried some Schneider easy 9's but they're a weird layout like loads...
  19. H

    Upgrade Tails & Bonding?

    Say you were going to change a CCU, and it is an 80A fuse with 16mm tails (10mm earth). Bonding is in place in 6mm. What would you do with regards the tails and bonding? Been thinking about this scenario all morning and it's bugging me now. I'll walk you through my thinking, would appreciate a...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top