Job is to install one or two new sockets in a commercial premises.
Possibly on a new radial circuit or an extension to ring.
If extension on a ring them a Minor electrical certificate is required together with all relevant testing.
However if a new radial circuit is the way a full EIC...
Apologies I know theres been a few threads about this and IR tests, but I'm still somewhat confused.
The way I understood how an RCD works is it measures the current flowing through the Line and the current flowing through the neutral on the return. If there is an imbalance of more than 0.03...
I was called by the client to do final live test & issue EIC. Not so straight forward, not all cable chases have been plastered and a couple of areas where boarding has still to be completed. So annoying, anybody else come across this?
hi
i have been asked to quote for a job where the owner is doing an extension and wants me to do all new wiring in the new part however he wants to keep the existing wiring the same.
he also wants to change over the cu to a new metal one (mk probably). What tests do people recommend i do on...
Hi Everyone,
Just a quick question, in the 18th edition wiring regulations book page 483 the schedule of tests results form it shows IR tests Live-Live & Live-Earth
Are they now going away from the Line-Neutral, Line-Earth & Neautral-Earth & just doing the combined test?
Thanks
Michael
Evening all
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to...
G'd Evening Lads an' Lasses,
I've got a Megger 1730 MFT; lovely bit of kit normally. Ex-demo - not had a hard life and was calibrated about eight weeks ago. I normally run it over a Cal-Card and a captive test RCD about once a month and this time it failed to trip the 30ma RCD on 1x, 5x and...
When doing an Electrical Condition report what's the best way to do a live to neutral I/R test on a lighting circuit with LED's (600x600) or infact any lights in a large office?
Hi guys got my assesment in 3 weeks and want to get my testing spot on. Little confused whether to test Zdb on 2 way CU before dead tests?? Or do I jump straight into continuity? Thanks in advance.
Other than the testing of the usual kitchen appliances that landlords supply as part of the tenancy agreement, I very rarely do any other PA testing. I will be carrying-out an EICR later this week on a property that will soon be made available to let. All appliances bar one are enclosed within...
Hi
When we bought our house a few years ago (which the wife said we would never move out of) I added a number of sockets to the upstairs ring final using some lovely surface mounted trunking. I did quite a bit of research at the time to make sure it was safe and tested them all with a plug in...
Hi Guys,
I work for a international packaging company and we have had a death of an engineer in South Africa. He was changing a motor on a strapping machine and electrocuted himself, further details are not for coming yet.
It has raised questions as follows and i was looking for your...
Hi all,
Customer reports sporadic nuisance tripping of RCD. I cannot reproduce it, or fault anything, except SOMETIMES on EFLI test it trips the RCD (megger mft 1553 'no trip' test).
I'm out of ideas here, can anyone help? This is what I've got:
- TT installation (small domestic);
- 30mA RCCB...
Hello all,
I've worked as a sparky for 3 years before now only deciding to do my tests, got level 3 unit 301 out of the way pretty quickly but dreading unit 302!!!! Any tips on what to revise formula wise? Am I going to need to know every formula??
Thanks,
Dan
Could you tell me whether most of the tests carried out for a Domestic Electrical Installation Report would have to be repeated if a replacement consumer unit is subsequently fitted?
Changed a consumer unit everything fine all test came back hunky dory, but one RCD would not trip on the test button so swapped them around, same deal,I then got random trips from unassociated circuits IE kitchen ring plug in kettle and the opposite RCD would trip disconnect incoming earth...
Hi guys,
Was wondering if anyone could shed any light on why I would be getting >2000 ohms on my loop tests, on every circuit? I got .26 on the incoming reading, went to do the test on the cooker circuit and >2000, thought I'd try back at the consumer on the incoming and >2000 again, I'm using...
Is the continuity test for circuit protective conductors, the same test for ring and radial circuits or is there a different test for each type of circuit?
Also what is the difference between testing for cpc continuity and testing for continuity for ring final circuit conductors?
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc