Hi,
We have a three phase 400v socket rated at 63A. It is proposed to use this for a mobile skid. There is an 18.5kw motor and an approximate estimate of current is 34A, the supplier is saying that the socket is not rated high enough as the skid has dual redundancy ( two 18.5kw motors) and as...
Has anyone had any experience of using these?? Any good??
Got a customer who wants to put a 3 phase 11kw chicken rotisserie into a shop with only a single phase consumer unit and doesn't want to spend 10 grand on getting a new supply.
Ive got my am2 resit tommorow for my live testing and I ran out of time and failed as well as I carried out the ze test on 2 lead high thus tripping the rcd.
So now I know for next time to complete this on a 3 lead LOW test and measure ze with earth disconnected etc.. then connect main earth...
I’ve been asked to calculate power usage of a machine to works out how much it costs to run.
Current draw is:
L1: 9.71
L2: 9.61
L3: 11.14
N: 7.78
Obviously when designing a circuit you would base it in the highest phase ampage.
But is power usage worked out the same way? Or are three...
Hi Everyone
I would be glad if you could clarify this for me:
For a Load Estimate Survey whereby 95% is single phase, the Load Estimate is 90 KVA (Single Phase). However, the power supply is three phase 4 wire system.
To calculate the current per phase, the 90 kVA is divided by three i.e. 30...
Hi all, been a bit of a lurker of the forums here for a while and so far they have saved me more times than I can say, but now I have a question that I am hoping you can help me with.
I have a single phase forklift charger and it currently has a 2p+e plug and connects to the corresponding...
Hi
I have recently moved into a small newly renovated (inc electrics) cottage and noticed appliances going really slow. Kettle taking an age to boil, toaster taking a long time, hair clippers going slow... you get the picture.
UK power networks sent an engineer that changed the overhead power...
Hi all
Need some help remembering some college work.
Been doing a job and we are pulling in 400mm singles in parallel, got three phases and a seperate earth but no neutral.
From what i remember from college was it becuase if you had the phases all balanced youd have no...
Hi i have just bought a lathe which is running on three phase i have bought a vfd to run the lathe from single phase
but i have a coolant pump that runs on three phase i have converted it to run on single phase but it appears to have a dip when running do any of you guys know what i need to do...
Hello all...hope someone here can help....
currently have three phases coming in to the property (old farm) but only receive single phase with a single phase meter. The overhead cables were upgraded a few years ago so the cabling up to the meter is all fairly recent, I can see the 3x100amp...
I will be enrolling on the NVQ3 2356 soon but have a question regarding the three phase element. As i work for agencys as an improver its seldom that I ever get asked to connect up three phase equipment, or test it. How have any of you previous students on the 2356 (mature candidate) found their...
Hi, need to ask a question about a 3 phase air condition. On it's data tag it is rated at 20Amps. When it rated like this are the 20amps on each phase?
Thanks in advance.
I am in the process of designing the electrical installation of a community centre, and have a question about the provision of three phase lighting for a large function room containing 18 36W LED fittings. All of the light fittings are to be switched simultaneously. Would it be possible to...
Hi,
Can anyone point me in the direction of the regulation / code for the max solar MCB size when connecting into a spare way of a local distribution board ?
Eg. Is it possible to connect a 100A breaker into a 100A board ?
[tl;dr] If an item of equipment wanted to draw 16A of current, would it be possible for something else to restrict this? i.e. If equipment wanted to draw 16A of current, is it possible it would only draw 10A (hence making it not operate as it should)? Due to something external of the...
I am attempting to produce a design for a theoretical installation with a three phase incoming supply (presumably Star/Wye with PME to star point), and am having some trouble understanding and determining the current and power of each phase, and the whole installation at the incoming supply...
hi.
one of the electrition in our company tried to wire a three phase pool air blower {in star connection}.
when he connected the three phases to the air blower after one minute the air blower coils were burned.
the thing is before that there was another of one phase air blower and it was...
Hi all,
Newbie here with no electrical experience so please be gentle! :blush:
I am currently refurbishing my basement flat and during this we have discovered that the supply to the four flats is single phase. I have been told this is unsafe and insufficient for the four flats. U.K. Power...
Hi there, I'm wondering if you gentlemen would so kind as to bless me with your wisdom.
Just to confirm, this is a question that I am attempting to answer as part of 304 of the 2365, so a point in the right direction with my answer would be mightily appreciated.
The exact question is...
I have an Install where a 16mm 4core has been installed previously. ATM the SWA is coiled up either end At the supply which is a barn converted in to an office for the homeowners business and plant room in new extension to the house. There is no PME available as over head, in the middle of no...