too

  1. Mr Mark Sparks

    how far is too far

    how far can a 50w lamp be from its transformer these will be surface spots and the transformer cant be local i can use any size cable i need to ,the furthest point will be about 10m away
  2. A

    LED Bulbs too bright - any ideas??

    Hi I recently installed 4 decking lamps for a customer - the customer supplied the lamps which are IP 56 rated sealed units, with 2W super LED bulbs. The customer has called to say they are extremely bright and do I have any ideas for making them less so. (he attaches no blame to me as he...
  3. S

    r2 readings too high?

    Are these readings for r2 (not R2) too high? kitchen ring: r1= 0.13 rn = 0.12 r2 = 0.33 cellar/living room ring : r1= 0.15 rn = 0.15 r2 = 0.40 Bedroom1 and 2: r1= 0.48 rn = 0.48 r2 = 1.17 what could be the problem if so? Thank you for your skills Si.
  4. N

    Is it too late for a change in direction?

    I am hoping that you experienced electricians will be able to advise me. I spent 17 years in the British Army as a Radar Technician having completed my Radar Apprenticeship. Since leaving the army most of my career has been spent in the Middle and Far East where I have installed and...
  5. P

    Not Sure what too do

    Doing a rewire at the moment. There are 2 boards, 1 is feed from the other. The main one has a 84amp RCD, and the one it feeds is a 64amp fuse, all this is from a 100 amp main fuse. now there is an isolator that comes off from "somewhere". Now the client wants me to change the Isolator for a 4...
  6. C

    Zs too high

    Hi After completing a 2 exta sockets in another kitchen, im finding the zs is on the limit. well just over. Zs - 1.06 (0.91 per OSG) I know the rcd helps with disconnection times but what would be my best option to bring this within limits, additional earthing to cu? The system is TNCS, with...
  7. G

    retraining at 41 - too late?

    OK, I am 41 and thinking of retraining. I have worked for BT for 20 years and have a HNC in electrical/electronic engineering. I am looking at doing a 2 year C&G 2330 evening college course. When I joined BT I thought it was a job for life but now sick of the management attitude, outsourcing...
  8. Dan

    Too many or not enough.....