Evenin all
Just a bit of an odd ball question here following a discussion i had today.
PVC twin & earth - If it is exposed to moisture or is laying in water over a long period of time, can this have a deteriorating effect on the cable sheath
Many thanks
Does anyone know where I can get one of these....
It slices the sheath down the centre of T&E. Looks like it has an adjustable size gauge on the top too. :cool3:
Been racking my brains all day and still can't figure out how a 6mm twin and earth has ended up burnt out as though having more current through than should the scenario
8.5kw/h electric shower
6mm2 t&e in trunking on wall
40a MCB with 30ma RCD Protected
The cable burnt at CU end and MCB has...
Hi everyone ive been to look at a board change in a two bedroom flat the db is supplied from a meter room with 10mm twin & earth via a 63 amp switch its a tncs system. The earth from the met in the meter room to the 63a isolator is 16mm but from there to the db is only 4mm coming from the 10mm...