volt drop | Page 6

volt drop

  1. brucelee

    working length of circuit from resistance for volt drop

    Hi all could someone please be so kind to explain how i work out the length of a existing ring final circuit 2.5/1.5 T/E and in turn Volt Drop i know to work out length its L= R x 1000 divided by m/ohm/m but would i use the r1 measurement eg 0.58ohms rn was 0.58ohms r2 was 0.96 or from the...
  2. I

    Volt Drop

    Hi, I am working on a unit with a large compressor and lighting on a single phase (bad design). When the compressor kicks in we get a volt drop noticeably dimming the lights. This is not acceptable so am trying to a work a solution. My preferred is just get everything on 3 phase, but not...
  3. S

    Volt Drop

    Hi I have a query one of you may know the answer to. I have installed some lights in the woodlands for a customer and he is using 12watt LED lights he is only installing a few i think it was 186 watts or something. I have used SWA cable 1.5 mm as it is about 200metres and worked out the...
  4. H

    Volt Drop in pv installs

    Hi Guys, Looking for a bit of advice re volt drop and PV installations as I'm getting confused. For example, a domestic job where the property has an outbuilding with a south facing roof. The customer already has a 100m length of 6 mm cable feeding the outbuilding. They wish to install a...
  5. J

    volt drop rule of thumb

    Hi Guys, could anyone explain to me the 1.2 volt drop rule of thumb? i understand the 3% for lighting and 5% for other circuits. any help would be welcome studying for 2391. Thanks in advance.
  6. L

    volt drop calc

    is this right mv on chosen cable from regs x length of cable run x design current of circuit divided by 1000 is it calulated amps or the breaer your going to use is that all as im trying to work out for this lighting circuit but to get the volt drop under 3% the cable needs to be 6mm ta...
  7. G

    Testing volt drop

    How do you guys record the volt drop? Measurement with volt meter Calculation with the mVA formula Other, please state
  8. P

    AC volt drop on pv system

    I am currently designing a 29kW system for installation on an agricultural barn. The PV system will feed into a 3ph db in the barn. The exisitng db is fed from a 63A fuse switch, approx 50m away with a 16mm cable. The fuse switch is in turn fed from the DNO cabinet approx 100m away with a 35mm...
  9. S

    Volt drop three phase

    When calculating volt drop on three phase, I can't remember if I my calculation is using the total current on all three phases or just each individual one. So each phase at 400v is 3.8A. My calculation was 2.5mm minimum. A three phase motor run in SWA. The run is 200M underground.
  10. B

    volt drop

    hi i have a long cablrun of 500m for a entry gate which possible will have a worm drive so current usage will be low.my question is i have to supply a 13A socket for remote working ect,this socket as not being used constantly should i calculate VD on the 13A which will be used 1 a year are on...
  11. A

    Confusion over the 1% volt drop on AC side

    Could someone please advise, is this to be calculated from the inverter to the main C/U, or could this be to a sub board?
  12. A

    Volt drop on spurred lighting

    I have a run of garden lights to wire up, roughly 1000w so about 4.3A. If they are on an rcd spur from the ring main, is the volt drop allowed for a lighting circuit (3ish %) or for ring main (7% is it)? As 100m at 4.3A will require 4mm if my calcs are correct for a 3% Vd.
  13. telectrix

    Volt Drop for Dummies

    done a quick excercise to give a rough guide. each cable is assumed to be carrying it's max. load, clipped direct, to give worst scenario, and a 10m length of cable. so the figures below represent the worst volt drop/10m 1.5mm ...5.8v 2.5mm....4.86v 4.0mm....4.07v 6.0mm....3.43v...
  14. B

    why is volt drop important???

    whats the reason we worry about volt drop? It cant be because of the design of fittings etc.. because the actual voltage can be 230v +10% -6% percent, i believe if there is a voltdrop then the current will increase as per ohms law maybe its something to do with potential differences e.g...
  15. J

    volt drop

    hi all i have been to collage today and we did a bit on volt drop. can some one plase help explain this to me? does this mean on a long run if the cable is not big enuf it will loose volts? eg. 221V?
  16. La Poste

    TT Earthing question// Volt drop

    Greetings. I have a question, this has been puzzling me for a while. If a put an earth rod in the ground and use it as my main earthing method and measure the resistance I find it to be 160 Ohms. Ok, Assume there are no RCD's and a link is made between the phase/line and earth at the...
  17. B

    can you check my volt drop

    hi all got a sud main to price 45A 27m 45A x 27m x 4.4mV/A/M for 10mm divid 1000 VD 5.34V now some of the circuits on submain are lighting mav VD 6.9V leaving only 1.56V for the lighting circuit. 6A x 20m x 44mV/A/M for 1.0 divid by 1000 VD 5.28 now am i right to say this sub main...
  18. D

    Calculating volt drop, cable selection and mcb selection on an 3kw motor

    Any explanations on how this is calculated ? Diversity : By referin to table 1b in the osg, it states : 100% largest motor ?? ...3kw ....??? 3000/230 = 13.04 A....is this it !!?? max demand ?? How there on would you make cable selection , mcb selection ?
  19. C

    Volt drop across 24awg cable

    this cable is 7 strand 0.203mm diam for each strand, metal braided screened. What would be the volt drop across 250 foot? Great site!!
  20. L

    Ring Main/ Volt drop

    Can anyone tell me where I'm going wrong..... Common knowledge 100m is max for ring final!!!! Im trying to work out volt drop for said length and I am way off where I need to be....... singles/trunking............15x32x100/1000=48v Yet if I put a radial in ....15x16x100/1000=12 Can anyone...