Hi guys,
Need to put a 32A 3phase supply in to a 10KVA site transformer using swa. The run is 250m long but would i need to apply 3% or 5% volt drop??
It works out at 3% i need to use a 35mm cable and at 5% i can use 16mm.
Anyone have any idea???
Thanks
Phaze-3
Hello there.
I'm trying to calculate the volt drop on cables that are over 16mm csa using the tables in BS7671. It's quite easy for lower sized cables, (length x design current x mV/A/m, if I'm right) but what happens when you go above 16mm and have a resistive component mV/A/m(r), reactive...
Hi Guys,
I haven't been on here for a while and was just wondering how most people are interpreting the DTI guide 1% voltage drop recommendation nowadays?
Is the only way to be 100% sure that inverters will not ever drop out to design to 1%?
And when meeting 1% requires enormous cable sizes...
hduz5
Thread
cable
electricians' talk
however
needs
voltvolt drop
voltage
volts
I've got a very well made 24 volt, 50 hertz, 81 watt pump, however I do NOT have a transformer/converter. I'm from down-under, so we run on between 220 to 250 volts. Is there a nifty trick one can do to get this thing running on 240 volts? Can I put a different transformer in-line with a...
A single phase power circuit supplying an item of equiptment, having a full load current of 25A, is to be checked to confirm voltage drop compliance , the circuit is to be installed using 6.00mm2 copper conductors, with a circuit length of 35m.
a) Calculate the maximum permissible voltage drop...
Martinm
Thread
circuit
confirm
electricians' talk
question
voltvolt drop
voltage
volts
Looking at the regs it says we have a supply of 230 Volts and so we do our calculations based on this so that if we had to install lights on the end of a long cable we would use a cable with a larger CSA and hence more cost.
The fact of the matter is we have a supply of 240 Volts so why do we...
Greetings.
Let's say you have a 2.5mm cable that you want to extend by quite a long run.
After looking at your load and volt drop calculations you arrive at a cable size for the extension of 6mm.
Would it be bad practice to add a 6mm extension to the end of a 2.5mm cable?
The circuit...