When selecting a cable and taking voltdrop in to acount is it 3% for lighting or 5% for other loads of 230v
Because the voltage obviously changes from anything from 216V up to 253V.
Thanks :)
When ticking the box for verification of volt drop on an innitial verification whats the procedure for this ?
Would you not need loads to be running to get an accurate reading?
Thanks simon :)
I am going to be installing a sub main from a house db (at meter position) to shed(1), then from that shed to shed(2), then from that to shed(3).
I am aware that lighting is max 3% drop (6.9v of 230v)
non lighting is max 5% drop (11.5v of 230v)
voltage under no load at supply...
Hello everyone just want a little help how you would calculate the volt drop if
230 single phase heater circuit
line & neutral conductors combined resistance of 0.68
Temperature at 20 degrees and load current of 16A?
show calculations
got this in my 2395 today wanna make sure I used the...
Hi, I am Nicholas, I repair computers from home for a low paying hobby and repair PC power supplies with the skill of replacing bulging capacitors. I will try other repairs using the same skill of desoldering and soldering, and I am living in a single flat here in Auckland NZ.
About 9 months...
eleNickBJ
Thread
connections
oven
switch
various
voltagevoltagedrop
volts
Hi everybody.
I have a question (still learning, passed 17th edition and part P, but I'm not yet registered).
If you use formula from On-Site Guide p.140 what the design current you put in the formula, to calculate max length of cable for 11.5V.
If 32amp then the maximum length of ring final...
yarcyk
Thread
around
formula
length
question
voltagevoltagedrop
volts
where
Its been along day, I've just finished off with looking around a big garden which has all sorts of electrical things going and would appreciate a bit of advice on VD.
Garden is supplied by 2.5mm SWA (buried), at present taking about 1000W from a 20A MCB in the garage CU. The chap wants 2...
Is there a voltage drop from DNO transformer to incoming supply? For a standard 100A supply to a house so they design cable to with stand no VD as so at maximum demand there will be no VD. It is then up to us to design circuits as to have as little as possible so that 230v remains everywhere. Of...
2395 question regarding voltage drop, cant tremeber the question but it basically asked what is the voltage drop for a 40 amp circuit at 230v with a combined live conductor resistance of .23 ohms any idea? it had me stumped.
thanks
ample current
Thread
circuit
question
resistance
thought
voltagevoltagedrop
volts
I'm having a bit of a blonde moment, I'm trying to work out the volt drop on a 3 phase Submain, the Submain is to be supplying a 3phase board loaded with rcbo's all single phase loading, I can't for the life of me remember how to do it I think it's working out the single phase vd and multiplying...
The voltage drop is causing the inverter to turn on and off like 50 times in the early morning and in the evening.
My grid tie Fronius IG 30 inverter is keep turning on and off like 50 times before it connects to the grid in the early morning because of the voltage drop. In the evening it...
cham cham
Thread
early
evening
get
morning
panel
panels
solar
solar panels
voltagevoltagedrop
volts
Hi, (new to forum, first thread)
Trying to get my head round voltage drop and using the calcs in practice.
I have radial circuit - 16 amp MCB on a 30mA RCD - 2.5 flat T+E out of household consumer unit, straight through wall and running in plastic conduit along outside of wall and into garage...
Gloster Boy
Thread
calcs
circuit
current
section
socket
voltagevoltagedrop
volts
Hi Guys, I'm fairly new to the industry and have sat and passed all the relevant exams to become a Domestic installer. I'm a little stuck with one of my pieces to be assessed by NICEIC. I'm doing a full rewire at my dads house and would like to check that I'm calculating the cable volt drop...
fire8789
Thread
calculating
correct
length
main
please
ring
ring main
voltagevoltagedrop
volts
hi was wondering what every ones opinions are regarding volt drop calculations i know there are 2 ways the ohms law way and the way where you use tables of the bs7671, the thing is i taught my self how to do volt drop calcs so i learnt the ohms law way is this a acceptable way or should i do it...
Good morning All,
Ive been asked to work out the potential volt drop on 12 metres of 10mm x 7 core SWA powering a 45kW (60hp) motor.
Just to check my findings as below, please could someone confirm whether I have done it right.
45kW - 80amp FLC
as using Star Delta Starter
multiply by...
i want to know the formula for voltage drop calculation for 3 core x50mm2 hv cable feeding 1000kva transformer 13.8kv. the cable is xlpe ,armored..it is connected from Ring main unit
hi guys, i have the 2392 practical assessment next month sometime and was wondering if anyone could confirm or remember if you have to verify voltage drop at the end of the test, I have been practising the calculations (mV/A/m) /1000 etc as well as going through the general test procedure but...
Hey all, reading through the 17th trying to get my head around some areas of it. I did physics at school and some at uni so electrical calcs usualy dont bother me the slightest.
BUT, If were calculating voltage drop over a reasonable length radial, for example twin and earth or SWA feeding a...
Hi all,
been trying to work this out now and carnt get my head round some of the calculations.
please see where im going wrong.
voltage drop:
so 63amp mcb supplying electric boiler, run is approx 25 meters in 16mm twin & earth.
so Mv/a/m x length x amps divided by 1000= 2.8x25x63 divided by...
aaelectric
Thread
earth
equation
meter
value
voltagevoltagedrop
volts