0.06 meg Ohm could it be a load | on ElectriciansForums

Discuss 0.06 meg Ohm could it be a load in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 27, 2019
Messages
57
Reaction score
6
Location
London
Would a load register as something like 0.06 Meg ohm on a circuit between N - E ( something like an unfused spur with the fuse removed? or is it just wishful thinking
 
I think you need to elaborate as how you have achieved this reading and the purpose of the test
Purpose is curiosity of my own electrical installation, and why i would have almost a dead short on N-E but with no RCD tripping unless it was a load

My flat has a circuit in it that tests as follows when live cpc and neutral are disconnected from the CU @ 250 volts

ZS 0.45

L-E >200 megohm
L-N >200 megohm
E-N 0.006 megohm
 
If it’s just the circuit you’re testing, N-E should be clear. Any load, even a neon light, would be between L-N

What is on this circuit?
Is everything unplugged if it’s sockets?
Is the polarity correct at each point on the circuit?
What are the readings at other points on the circuit?
 
If it's a radial circuit e.g. cooker/shower/maybe immersion then have you tried turning the isolator off near the load?
I'm having a stab in the dark that this is a heating element.
 
I have seen this with an old RCD socket - it had something like 50k to E as a means to trip out in the event that neutral is open or swapped.

But it could be some faulty cable of course, which is more worrying. You need to see if any loads were still connected during the test as there was only SP isolation on them.
 
60KΩ isn't going to be a design load for an appliance, do the maths and that's an Ib of 3.8mA which is daft. It could though be a Neon?
 
60KΩ isn't going to be a design load for an appliance, do the maths and that's an Ib of 3.8mA which is daft. It could though be a Neon?
agreed, I was wondering if it was a element deteriorating N to E as 3.8ma leakage seemed plausible.
I should be patient and wait and see what the circuit is!
 

Reply to 0.06 meg Ohm could it be a load in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
356
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
389

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top