0.75mm2 flex for fixed equipment - reality check. | on ElectriciansForums

Discuss 0.75mm2 flex for fixed equipment - reality check. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 28, 2012
Messages
358
Reaction score
115
Location
Aberdeen
Hi Folks

I've never thought twice about using 0.75mm2 flex for connecting fixed equipment (e.g. extractor fan in window) to a fused connection unit with 3A fuse where this is sufficient for the load of the equipment. But table 52.3 of BS7671 states minimum csa for copper cable in lighting circuits as 1.0mm2 and power circuits as 1.5mm2. The 18th edition even adds 'Note 4', which states "For lighting circuits and associated small items of current-using equipment, such as a bathroom extractor fan".

So am I wrong to use 0.75mm2? Or does the FCU take the place of a plug and mean I can use this? This has come up as I have bought an RF remote switch for a customer's outside lighting and this has 16mm glands that will not accept 1.5mm2 flex. I don't have any 1.0mm2 to try, but pretty confident that wouldn't fit either. The remote switch is obviously intended for permanent installation. I'm interested in the answer generally, as well as for this specific piece of equipment - essentially, does the presence of a fused connection unit negate table 52.3?
 
Hi Folks

I've never thought twice about using 0.75mm2 flex for connecting fixed equipment (e.g. extractor fan in window) to a fused connection unit with 3A fuse where this is sufficient for the load of the equipment. But table 52.3 of BS7671 states minimum csa for copper cable in lighting circuits as 1.0mm2 and power circuits as 1.5mm2. The 18th edition even adds 'Note 4', which states "For lighting circuits and associated small items of current-using equipment, such as a bathroom extractor fan".

So am I wrong to use 0.75mm2? Or does the FCU take the place of a plug and mean I can use this? This has come up as I have bought an RF remote switch for a customer's outside lighting and this has 16mm glands that will not accept 1.5mm2 flex. I don't have any 1.0mm2 to try, but pretty confident that wouldn't fit either. The remote switch is obviously intended for permanent installation. I'm interested in the answer generally, as well as for this specific piece of equipment - essentially, does the presence of a fused connection unit negate table 52.3?
Table 52.3 also makes allowances for non sheathed and sheathed flexible cables as specified in the product standard,for any other applications and for extra low voltage circuits all with a minimum CSA of 0.75mm
 
The regulation refers to the circuit cable protected by the OCPD in the DB, not a flex from a local point of connection serving a load. Think of a pendant flex, often 0.5mm or 0,75mm
Thanks Wirepuller, makes sense. And the pendant doesn't even have its own OCPD like an FCU. But don't you mean downstream? Or is my brain still malfunctioning?
 

Reply to 0.75mm2 flex for fixed equipment - reality check. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

  • Question
There is no reason for an item of fixed equipment to be on its own dedicated circuit just because it is fixed equipment. There may be other...
Replies
2
Views
481
loz2754
L
As a trainee, one of the things I've tried to focus on to deepen my interest in the world of electrics, is the space for creativity. I've...
Replies
0
Views
313

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top