A disused fused switch was connected to a boiler that was removed. The wire running to the switch was 2.5mm and the person wants a socket to run a tumble dryer (2300w). This is the only device that can be connected to the cable.
When checking the CU, it appeared that it was 1.5mm connected to a 6A mcb (B type). I am rechecking as it's next to a 10mm so might have looked a bit deceptive. It appears that the cable run is very small (3 mts) as it goes into wall and out.
I could use a 10A or 16A (to allow for start up current) in place of the 6A which would leave only 2amps for cable (17.5 Imax Table 4D1A method 3). This seems a little close to maxing out cable (using 16A) for me and heavy loading of the mcb (using 10A)
The alternative is to start pulling up carpets and floor boards and running a new cable adding to cost and time for client.
Any suggestions (sensible) as best way to approach this
Cheers
 
Ah think we should all go to the pub and discuss this topic lads as my wife disnae like it when I talk work when we're invited to somebody's hoose. It would be great to talk about our 'metier' all night in the partaking of a few beers, no?
 
A Saudi cleric has forbidden it though. He can sod off :)
...Let us not forget,religious zealots come in all shapes...when i was in my early teens,i had a maths tutor (poor folks had such high hopes...) anywho,she told my parents,that if they allowed me to watch "Life of Brian",i WOULD burn in hell...

She was an eighty year old anglo saxon ex-ballet dancer spinster.....and THE worst driver i have ever seen,here or abroad:icon12:
 
...Let us not forget,religious zealots come in all shapes...when i was in my early teens,i had a maths tutor (poor folks had such high hopes...) anywho,she told my parents,that if they allowed me to watch "Life of Brian",i WOULD burn in hell...

She was an eighty year old anglo saxon ex-ballet dancer spinster.....and THE worst driver i have ever seen,here or abroad:icon12:
Oh crikey yes, every religion has it's idiotic zealots. Just look at the Westboro Baptists for an example.
 

Reply to 1.5mm cable loading in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
438
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top