Hello good people.
I have an ongoing issue with a top entry immersion heater over heat stat that keeps Tripping out. (Built into stat) On a 24hr mechanical timer.
The tank was replaced just over a year ago and with it a new immersion heater and stat.
The original stat worked fine for about 3 months then the O/H stat tripped. I did some tests and all came back good so I reset it and went on my way.
About a month later it did it again so I returned and did the same again. This time it worked for about a week and tripped again.
So I replaced the stat and all was good for about another 3 months or so, then got called to it again.
Tested it again and the circuit and all was the same as the previous test, I put it down to a bad stat and swapped it under guarantee.
Again it was fine for a while about 4 months or so and it did the same again.
I went back with a plumber and we spent a good couple of hours playing around and couldn't get I to trip out, so we left and all was fine until about a week ago when I got called to it.
Again it was tested and all results were good so I replaced it once more with a different make.
Got called to it this evening again thermal overload tripped!
I have run out of ideas, usual things checked, stat set to 55 and is cutting out at that.
Insulation resistance test came back 999m ohms on the circuit and heater hot or cold, element resistance 21 ohms, earth loop 0.33 ohms, voltage 241v.
All connections checked for tightness.
Any other ideas guys?
Cheers Sy
I have an ongoing issue with a top entry immersion heater over heat stat that keeps Tripping out. (Built into stat) On a 24hr mechanical timer.
The tank was replaced just over a year ago and with it a new immersion heater and stat.
The original stat worked fine for about 3 months then the O/H stat tripped. I did some tests and all came back good so I reset it and went on my way.
About a month later it did it again so I returned and did the same again. This time it worked for about a week and tripped again.
So I replaced the stat and all was good for about another 3 months or so, then got called to it again.
Tested it again and the circuit and all was the same as the previous test, I put it down to a bad stat and swapped it under guarantee.
Again it was fine for a while about 4 months or so and it did the same again.
I went back with a plumber and we spent a good couple of hours playing around and couldn't get I to trip out, so we left and all was fine until about a week ago when I got called to it.
Again it was tested and all results were good so I replaced it once more with a different make.
Got called to it this evening again thermal overload tripped!
I have run out of ideas, usual things checked, stat set to 55 and is cutting out at that.
Insulation resistance test came back 999m ohms on the circuit and heater hot or cold, element resistance 21 ohms, earth loop 0.33 ohms, voltage 241v.
All connections checked for tightness.
Any other ideas guys?
Cheers Sy