I work for a housing association and we've been told that any shower above 8.5Kw MUST be wired in 10mm cable. Seems excessive to me as it depends on derating factors as mentioned above. Lots of cursing at work!!

I know it's a pig to work with isn't it. Big fat cable in fiddly little normal fittings. I have cracked many a patress trying to persuade the cable to do as its told in a ceiling isolator ......
 
That is why we have "good practice" but aswell as our actual rules and regs. Over 9Kw 10mm for me everytime.

This is not facecious, but a serious question:
I really want to know from someone who does, why do you insist on fitting larger cable than the calculations and tables in 7671 state is necessary? What percieved 'advantage' do you believe you or the client are gaining?
 
This is not facecious, but a serious question:
I really want to know from someone who does, why do you insist on fitting larger cable than the calculations and tables in 7671 state is necessary? What percieved 'advantage' do you believe you or the client are gaining?
one word answer..... overkill
 
been in trade 7 years, fresh out of college just 1 year though. went in thinking i knew everything i needed to, came out realizing i still had loads to learn and still am. this has been an issue with most the sparks i've worked with. The one company i do work for insist i come out of fused spurs(from load side) with 2.5 to any other spurs or sockets despite me telling them 1.5 will do but all i get is a condecending "just do it". the way i look at it is if its safer and you're paying then its ok, but if i'm paying i'll do it to the regs.
 
This is not facecious, but a serious question:
I really want to know from someone who does, why do you insist on fitting larger cable than the calculations and tables in 7671 state is necessary? What percieved 'advantage' do you believe you or the client are gaining?


I suppose for me over design is peace of mind .
Every one is on the insulation war path now days , if it dont move insulate it .
That length of 6mm may be good today but next week it may be in a rock wool bath !
If the job is that tight on margin to make it undo able then we wont !
As for the advantage they gain , when their new 10kw shower packs up in a few years time they will be over the moon that they can fit the next size one up that is then out with no re dec required .
Who would have thought 10 kw would be main stream even ten years ago !
 
but who knows what will be main stream in the next 10 years. things are drawing less and less power now but giving better performence. you can only design a circuit to the clients requirements and you charge them accordingly. if i charge a fee for larger cable size than neccesary then i could lose the job.
 
but who knows what will be main stream in the next 10 years. things are drawing less and less power now but giving better performence. you can only design a circuit to the clients requirements and you charge them accordingly. if i charge a fee for larger cable size than neccesary then i could lose the job.
Fair point !
 

Reply to 10.5kw shower run off 6mm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
352
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
901
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Can to OP clarify if this extension is just another room on the side of the building (so multiple cables going through the walls for lights...
Replies
6
Views
982
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top