Hi
I have a problem on a site that I have inherited.
The fault is that a 100A MCCB is tripping indeterminately.
The MCCB feeds a DB which has several cct’s none any higher than 32A and all cct’s are RCBO’s the RCBO’s are not tripping yet the MCCB is.
The MCCB has been changed recently.
Ahead of connecting up a Power Quality Digital Storage Oscilloscope which incidentally I haven’t got.
Any ideas?

PatH
 
Where is PatH?
is it single pole or 3/4 pole ?
what type is the outgoing cable?
 
Last edited:
I'm going to assume this is a 3 phase MCCB, if so have you checked the load balance (eg, is there one phase grossly higher loaded than the other two phases, does it have adjustable parameters, if so are the settings correct? Does it have earth fault protection, again is the setting(s) correct....


If all the above is fine then take regular amp clamp readings throughout the day, or hire a power analyser, because it would seem that on at least one phase the MCCB is seeing an overload....
 
I'm going to assume this is a 3 phase MCCB, if so have you checked the load balance (eg, is there one phase grossly higher loaded than the other two phases, does it have adjustable parameters, if so are the settings correct? Does it have earth fault protection, again is the setting(s) correct....


If all the above is fine then take regular amp clamp readings throughout the day, or hire a power analyser, because it would seem that on at least one phase the MCCB is seeing an overload....

Hi Guys

Thanks for your comments
I have tried most everything that you have mentioned
Loading on the 3 phases equal
Terminations are tight
The MCCB is not adjustable
The temperature of the cables are not excessive
The MCCB is the magnetic type so it is susceptible to a current crest factor 141.14amps on this breaker.
I have a suspicion that it may be this that is the problem. I also have the suspicion that the MCCB trips on start up in the morning. (This is very hard to judge as it does not happen every day) One of the cct’t from the DB feeds a gondola with a number of phones, chargers and associated electronic equipment. I did ask the store to leave this cct off for a fortnight to see if the problem went but they had various visitors in which they could not carry out this request. I have tested this cct for Zs and IR and all is fine also the RCCBo does not trip on this cct.
I think I probably will have to clamp the phases as the store starts up in the morning and turns everything on.

PatH
 
Hi Guys

Thanks for your comments
I have tried most everything that you have mentioned
Loading on the 3 phases equal
Terminations are tight
The MCCB is not adjustable
The temperature of the cables are not excessive
The MCCB is the magnetic type so it is susceptible to a current crest factor 141.14amps on this breaker.
I have a suspicion that it may be this that is the problem. I also have the suspicion that the MCCB trips on start up in the morning. (This is very hard to judge as it does not happen every day) One of the cct’t from the DB feeds a gondola with a number of phones, chargers and associated electronic equipment. I did ask the store to leave this cct off for a fortnight to see if the problem went but they had various visitors in which they could not carry out this request. I have tested this cct for Zs and IR and all is fine also the RCCBo does not trip on this cct.
I think I probably will have to clamp the phases as the store starts up in the morning and turns everything on.

PatH
Did you just make that bit up?
 
Unless your peak load current is very close to the MCCB's 100A or unless there's large motor drives on the load I doubt that crest factor is the problem.
 

Reply to 100 A MCCB feeding DB with various RCBO's tripping before they do? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top