E
Engineer54
Hi Guys
Thanks for your commentsI have tried most everything that you have mentioned
Loading on the 3 phases equal Terminations are tightThe MCCB is not adjustable
The temperature of the cables are not excessive What about the ambient temp of it's enclosure?
The MCCB is the magnetic type so it is susceptible to a current crest factor 141.14amps on this breaker. All standard MCCB's have both thermal and magnetic element trip release's
Ihave a suspicion that it may be this that is the problem. I doubt that assumtion I also have the suspicion that the MCCB trips on start up in the morning. (This is very hard to judge as it does not happen every day) Wouldn't the store manager know if the DB is tripping out first thing in the morning One of the cct’t from the DB feeds a gondola with a number of phones, chargers and associated electronic equipment. I did ask the store to leave this cct off for a fortnight to see if the problem went but they had various visitors in which they could not carry out this request. I have tested this cct for Zs and IR and all is fine also the RCCBo does not trip on this cct. I think I probably will have to clamp the phases as the store starts up in the morning and turns everything on.
Any Air Conditioning in this store by any chance?? If so is it a central unit or more than one smaller split AC units?
What's the max current draw on the 3 phases that you have measured?
Why not get this store to invest in a weeks hire of a power analyser, a decent analyser will a clear indication of what's going on within several parameters, not just current draw.... The forum sponser hires such analysers, give them a ring for a quote
Last edited by a moderator: