What is the purpose of 100 mA RCD ?
Where is requied ?
Where is requied ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 100 mA RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
usually on a TT system. there are other applications, e.g. for fault protection where Zs values exceed the max. levels for ADS with fuses or MCBs.What is the purpose of 100 mA RCD ?
Where is requied ?
I thought 300mA was for fire? 30mA additional, 100mA TT and 300mA for fire?As said above, for typical domestic application as already said it typically is the incomer on a TT system and normally is the delay (S type) version to downstream 30mA RCD have a chance to clear faults without taking out the whole system. Few TT systems will have a low enough Ze to allow adequate disconnection by even a 6A MCB, hence an RCD is often essential.
Also they are sometimes used for fire protection in agricultural setups even with a TN supply when cables being chewed by rats, etc, are a high risk. There you need a high current to avoid spurious trips, but you want to quickly disconnect on an insulation fault / roasting rat before it starts a fire.
Very common scheme for us is that we'll have a 400a/3 primary distro coming straight off a generator and it will have either an adjustable RCCB or an RCM/RCCB setup where both time and current curves can be set digitally as required. This also makes for interesting entertainment sometimes as if you're working in a damp environment for example overnight the cumulative leakage can go very high indeed, easily into 2-3A per phase, then at breakfast you watch them all drop back to something sensible as the sun rises and the air dries!! But...... that requires a whole heap of experience and know-how to keep safe, as I know Dave will agree with me on.you can also get RCCB style RCD units that can be set up to 5A and longer delay.
I think a 100TD S type is best for up front TT. A 100ma has a max of 300ms discon, a 100TD S type has a max of 500 ms discon.I thought 300mA was for fire? 30mA additional, 100mA TT and 300mA for fire?
It depends on what you are protecting, and how much it is expected to leak "normally" versus "faulty".that is interesting because why would you use 100mA when you could put 30mA, except type S for distribution circuit.