So a conversation with a fellow spark brought into question what exactly are main switches?

Is a 100A main switch a 100A double pole MCB or does the 100A mean its breaking capacity? I'm sure it's the former but I'm beginning to question my own knowledge as he thought differently.

Also, with different rated RCDs, 25, 40, 63...etc, Does that mean that it will trip if the current passing through it exceeds that amount essentially acting as an RCBO? If so, why do we need RCDs to double up as overcurrent protective devices as well?

This is probably quite a basic question but the reason we wondered is because we all seem to fit CU's with 100A main switches even when the cut out fuse is only rated at 60A or 80A. If the main switch is indeed a 100A overcurrent protective device, why is this?
 
So a conversation with a fellow spark brought into question what exactly are main switches?

Is a 100A main switch a 100A double pole MCB or does the 100A mean its breaking capacity? I'm sure it's the former but I'm beginning to question my own knowledge as he thought differently.

Also, with different rated RCDs, 25, 40, 63...etc, Does that mean that it will trip if the current passing through it exceeds that amount essentially acting as an RCBO? If so, why do we need RCDs to double up as overcurrent protective devices as well?

This is probably quite a basic question but the reason we wondered is because we all seem to fit CU's with 100A main switches even when the cut out fuse is only rated at 60A or 80A. If the main switch is indeed a 100A overcurrent protective device, why is this?

A main switch provides no overload protection and an RCD also provides no overload protection.

A 100A main switch isnt a double pole MCB nor does it have 100A breaking capacity. An isolator is an OFFLOAD device.

Ok, so in that case, why are there RCDs with different ratings? Why are they not all 100A?

What about for currents over 100A??...


Basics my friend....
 
Last edited:
I find it staggering that an approved electrical contractor would not know these details.
Truely speechless.

I agree with the above post, frightening that you sign off work

I do apologise guys, it seems I'm in the wrong job! I didn't realise that to be an electrician you had to know everything. Anyway, I'm off, I've got to start job hunting as clearly I'm not cut out for this electrical malarky.

I assure you both that in my new line of work, whatever that may be, I'll be sure to remain ignorant.
 
Erm it isnt About knowing everything , however knowing basics like that is a given

So yes if you didnt know that a main SWITCH is not a breaker you are in the wrong job pal, i take it your another one who doesnt have nvq level 3?
 
vernam616 i think you are being slightly harsh, we all come on here to learn and better ourselves yet you make rash comments? I Think you should go a little easy as maybe one day you might require someones help to a question you are unsure of.
 
Jesus christ get real man, theres no wonder Electrical Trainee get away with it because the world is full of people like you, i can imagine an apprentice asking this sort of question and id gladly answer them, however not an APPROVED CONTRACTOR, boils my blood it really does, someone who signs off work saying its safe is asking whether or not the main switch is a breaker

Your on the same level
 
Erm it isnt About knowing everything , however knowing basics like that is a given

So yes if you didnt know that a main SWITCH is not a breaker you are in the wrong job pal, i take it your another one who doesnt have nvq level 3?

I've no NVQ 3 but still know the difference between an MCB, RCD and an isolator:freak:
 
a few harsh comments here. OK, maybe a fairly basic question, but gaps in learning have to be filled at some time. i don't know exactly how a differential gear works, but i can still drive round corners. i don't know how my typing on here gets converted to 1's'and 0's and back to words to your pc/iphone/laptop, but that doesn't mean i can't communicate.
 
NVQ 3 maketh the spark

Whats this obsession with nvq 3 or whatever else is the current fasion
There has never been and likely never will be a definition of what constitutes an electrician

I call myself an electrician ( others can describe me as whatever they feel is suitable) I know or want to know nothing of this nvq fad,I take it that it is an installation course

Being an electrician used to be about being able to operate in maintenance or installation
In that maintenance role,fault finding and assessment of safety (test and inspection) was and probably is part of the job
When installing electrical systems and equipment.yes we used to do both. Electricians had one day to wire a house and the next install conduit or pyro or tray etc in an industrial workplace and the next go and fix a complex broken down machine
If we were presented with an armoured cable,( the type that most nowadays dont even see)we may ask, is it double wired paper insulated ? or perhaps lead sheathed ? we had skills for wide ranging activities

We also tried, as best we could, to keep up with modern practices and technical knowledge

There were good sparks,average and some who should have never been in the job,but there never was a defined piece of paper or even an organisation and that includes the JIB, that determined the role (the role of electrician was around for eons before this over hyped young JIb system was dreamed up)yes it is very short lived


No definition of electrician is the reason these days we have short course sparks, and also sparks, like some I could name on this forum, who in a way have no right to call themselves electricians, because their knowlege and abilities go way beyhond an average spark

In this wide ranging field of electrics,it is impossible to be a know it all
The various roles that members of this forum perform in and succeeded by making it the top,it shows this is a forum for sparks of all experiences and abilities

There may sometimes be anger and frustration at quick fix training etc,but that is the way of the world and it will continue

The opening post seemed to contain obvious gaps in knowlege and there is no doubt,he needs to knuckle down to his definitions,but who are you to say he is not an electrician,he may very well and probably does do an excellent job,we can never know, insults like saying get another job shows lack of understanding of your own trade,because of the variation of that trade

To any who deem it OK to throw around the superior attitude I say beware your comments dont come back to bite you
Even the high achievers. I have seen them make simple and surprising comments at times,all are fallable

Its time that judgement and personal critisism was laid to rest,because who in the end are you to judge what constitutes a spark


Why I have written the above,is to try to demonstrate to some.who have the opinion that a piece of paper or experience in a section of the industry suddenly gives them the right to determine who or what constitutes an electrician,it has never been defined
 
Very well said Des. I have just scrapped my own post on similar lines because I couldn't put it any better than that.

I will say however that I for one am sick to death of reading comments from the worlds best Electricians who's only point in posting is to rubbish someone else's opinion, and I am sure there are lots of others who share my opinion.

This problem seems to be getting worse, if you don't like a post, just move on to the next one.
 
I agree that some of the comments were harsh, but these are things that I would definately raise an eyebrow at if a self employed domestic installer said them to me. I would say some knuckling down and revision is a very good idea indeed. Every sparks should be aware that every item of electrical equipment has ratings of the voltages and current it is designed to carry. How can you use them properly if you don't ?

We are all learning every day however, no matter our experience. This forum is for questions to be asked and answered. I am a new member so don't know if this is the way round here, but a lot of people come in for abuse when asking for help. How helpful is that really ?
 
D Skelton, just for some info, maybe interesting, maybe not. On 3 phase distribution boards you do get MCCB incomers, RCD incomers, and switch disconnectors that fit in the same board, although this will differ by brand. Domestic CUs main switches are just switch disconnectors however.
 
Erm it isnt About knowing everything , however knowing basics like that is a given

So yes if you didnt know that a main SWITCH is not a breaker you are in the wrong job pal, i take it your another one who doesnt have nvq level 3?

Jesus christ get real man, theres no wonder Electrical Trainee get away with it because the world is full of people like you, i can imagine an apprentice asking this sort of question and id gladly answer them, however not an APPROVED CONTRACTOR, boils my blood it really does, someone who signs off work saying its safe is asking whether or not the main switch is a breaker

Your on the same level

For the record, I'm no Electrical Trainee, but who are you to question the job I do and why on earth should I have to come on here and have justify myself to you?! I worked dam hard to qualify as an electrician, excelling above and beyond my fellow students at the time! I have gaps in my knowledge yes, I'll be the first to admit that, but I'm also sure I have knowledge in other areas of eletrical work that would far surpass yours. I guarantee that some of your gaps in knowledge would be what I would consider to be basic but I assure you that you wouldn't catch me on here shooting you down for asking a basic question.

You badger on about the importance of an NVQ and yet you only completed your 2391 last month where as I completed it years ago! A qualification that many regard as having much greater importance than the NVQ. Not that I proclaim to be an expert because of one poxy qualification!

I know that a 100A main switch is double pole, I know that it is rated to only carry 100A, I know that it is suitable to provide isolation, I know it is linked and I know when I do and don't need one. I also thought for a moment that it might have functioned as a breaker, whooptie doo!

If I'd never have asked, I'd never have known, and funnily enough, no one at college ever explained to me exactly what a main switch is. If this is such crucial knowledge, tell me why no one ever thought it neccessary to tell me whilst I was studying??? Probably because it doesn't matter in the grand scheme of things!

Although it's good to know for example exactly how an RCD works, why is it neccessary? As long as you know where the regs tell you to put one, and what type it should be then there's never going to be a problem is there.

You sir have not been helpful or informative in any way, you have not advised me or even made known a professional or useful opinion. You have written nothing but abuse, and for no reason at all?! My only question is what made you so insecure that you had to shoot down a fellow qualified electrician? Saying that, I don't even care, I have nothing more to say to you and I can proudly welcome you as the first member of my ignore list!

Finally, special thanks to Des and to all of you who have either educated me, informed me or even just stood in my corner. I salute you all :)
 
Last edited:
D Skelton, just for some info, maybe interesting, maybe not. On 3 phase distribution boards you do get MCCB incomers, RCD incomers, and switch disconnectors that fit in the same board, although this will differ by brand. Domestic CUs main switches are just switch disconnectors however.

Thank you Andy, I am aware of this :)
 

Reply to 100A breaker? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
786
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
488
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top