first this i would do is look outside is the supply TT or TN-C/-S as for the lighting tripping a high inductive load found in fluorescents can cause tripping. Your best bet is to do a visual inspect of the enviromet that the installation is within and tell the client that you recommend a condition report be carried out. Village halls have groups of " freinds of " who carry out repairs and maintenance and on the other hand it sounds old probally still has original wiring within somewhere the possibilities are endless but the condition report will be the best option to find what your dealing with otherwise your end up being a dog chasing its tail
 
Do a full day free inspection (visual) bit of testing etc load clamping...... just to get you bearings, explain this will be free as you never know in the future when a village hall might come in handy for a family do'. ;)

But would deffo as reef said be looking at the lighting and possibly inductive inrush.
Do a count up and size and type of lamps, i bet if inductive you can simultaneously switch all banks on at same time and get front end to trip where-as one switch at a time wont show an issue.
 
Three weeks and still no results of any testing. Do you have the necessary test kit or are you working on guesswork?
Plenty of wild guesses from all sides based on no information.
 
Well said Tony! I've stayed out of this thread for exactly that reason. I'm amazed the number of recent OPs who are prepared to spend any amount of money substituting component parts to try and find a solution, but will not get the test equipment out and do even the most basic of tests. In at least one case, actively taking on work without possessing any test gear at all and did not see a reason for any. When they get into difficulties, unable to solve their problems, they start a thread on the forum and expect us to be clairvoyant. If this a representative sample of the calibre of Electrician currently coming of the production line; heaven help us all!
 
Too true, amazing how people have to consult a forum to fault find, i usually just go get my test kit out because....... Im an electrician and thats what im trained to do

You should do the same OP
 
Your not going to know anything, until you get your test kit out and start going through the system. Just wondering how dedicated circuit RCD'S can trip out the whole DB?? Another reason why you don't always take notice of anyone that has unreliable knowledge of what's happening and when... At the moment no-one can advise you on what's causing the fault(s), the permutations being too many!!

Engineer54 is spot on. Until you get your test kit out and/or experience it yourself, then take what's described as 'background info only not to be relied on'. My experience of 'information via committee' has not been very reliable in the passed!
 

Reply to 100A main breaker tripping with low loading? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
439
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
747
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
Norcal - thanks, belatedly. 'Tis the season when I don't get anything done, even though this project is near the top of the list. Per your...
Replies
7
Views
508
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
409

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top