So here's what happened.......
Was in a main intake room for a school comprising several outbuildings, and in the process of upgrading the entire switch room. The installation was ancient, and had rows of switch fuses all unlabelled.
Had to identify them for the upgrade so turned one off, which we found was isolating the kitchen block. So far all well and good. Turned it back on , only for the caretaker to tell me his fridges weren't on any more, but the lights were. Turns out somehow by turning it on and off, 2 of the three 100A HRC fuses had blown
I put this down to startup current on aged fuses, as there was no bang or any other indication of a fault
Ok , so we had lost two phases, which needed to be reinstated so the food in the fridges/freezers didn't spoil. Didnt have the correct specific fuses on my person (who would?), so put standard 30 amp fuse wire into the fuse holders to give a temporary supply overnight until I could get to the wholesalers tomorrow.
Went to turn the isolater back on and found the handle was a little stiff, but then they sometimes are... I gave it a more forcefull turn ( in hindsight not a good idea) and KABOOM! The isolater burst into flames which burned blue for a good five seconds and ran up the wall, and the entire switchroom filled with smoke!
When it all cleared (and after I changed my trousers) Only 1 200 amp fuse had gone in the main isolater, and the 400's in the head were all intact. Needless to say the isolater was completely cabbaged, so I disconnected it from the main bus bar until I can get my tester onto the submain it supplied (currently away being calibrated), although I have a hunch the fault was inside the isolater which was a make I've never seen before (DB was the make)
Anyway , hope you guys had a better day than me
Was in a main intake room for a school comprising several outbuildings, and in the process of upgrading the entire switch room. The installation was ancient, and had rows of switch fuses all unlabelled.
Had to identify them for the upgrade so turned one off, which we found was isolating the kitchen block. So far all well and good. Turned it back on , only for the caretaker to tell me his fridges weren't on any more, but the lights were. Turns out somehow by turning it on and off, 2 of the three 100A HRC fuses had blown
I put this down to startup current on aged fuses, as there was no bang or any other indication of a fault
Ok , so we had lost two phases, which needed to be reinstated so the food in the fridges/freezers didn't spoil. Didnt have the correct specific fuses on my person (who would?), so put standard 30 amp fuse wire into the fuse holders to give a temporary supply overnight until I could get to the wholesalers tomorrow.
Went to turn the isolater back on and found the handle was a little stiff, but then they sometimes are... I gave it a more forcefull turn ( in hindsight not a good idea) and KABOOM! The isolater burst into flames which burned blue for a good five seconds and ran up the wall, and the entire switchroom filled with smoke!
When it all cleared (and after I changed my trousers) Only 1 200 amp fuse had gone in the main isolater, and the 400's in the head were all intact. Needless to say the isolater was completely cabbaged, so I disconnected it from the main bus bar until I can get my tester onto the submain it supplied (currently away being calibrated), although I have a hunch the fault was inside the isolater which was a make I've never seen before (DB was the make)
Anyway , hope you guys had a better day than me