C

Crosswire

So here's what happened.......

Was in a main intake room for a school comprising several outbuildings, and in the process of upgrading the entire switch room. The installation was ancient, and had rows of switch fuses all unlabelled.

Had to identify them for the upgrade so turned one off, which we found was isolating the kitchen block. So far all well and good. Turned it back on , only for the caretaker to tell me his fridges weren't on any more, but the lights were. Turns out somehow by turning it on and off, 2 of the three 100A HRC fuses had blown:confused:

I put this down to startup current on aged fuses, as there was no bang or any other indication of a fault

Ok , so we had lost two phases, which needed to be reinstated so the food in the fridges/freezers didn't spoil. Didnt have the correct specific fuses on my person (who would?), so put standard 30 amp fuse wire into the fuse holders to give a temporary supply overnight until I could get to the wholesalers tomorrow.

Went to turn the isolater back on and found the handle was a little stiff, but then they sometimes are... I gave it a more forcefull turn ( in hindsight not a good idea) and KABOOM!:eek: The isolater burst into flames which burned blue for a good five seconds and ran up the wall, and the entire switchroom filled with smoke!

When it all cleared (and after I changed my trousers) Only 1 200 amp fuse had gone in the main isolater, and the 400's in the head were all intact. Needless to say the isolater was completely cabbaged, so I disconnected it from the main bus bar until I can get my tester onto the submain it supplied (currently away being calibrated), although I have a hunch the fault was inside the isolater which was a make I've never seen before (DB was the make)

Anyway , hope you guys had a better day than me
 
Had the same 25 years ago with the 12 way 100A consumer unit taken off a 700A busbar. I put the board cover back on not realising that the tail were coming through a 25mm ungrommeted hole and it went bang. At first the main fuse did not trip the cable just arced then it went bang.

With great bravadoe me thought that was lucky got a bit stunned and went home woke up with my eyes stinging and blind at 1:00 in the morning turned out I had welders flash and could have been blinded so lesson learned.
 
Last edited by a moderator:
Sorry to hear of the botty squinting episode. Reinforces the importance of regular inspections. Council H&S might be interested therefore more regular inspections therefore more work , oh and better safety!
 
I had this little mess to sort out

An night shift electrician was doing preventative maintenance on a motor control centre (MCC). At some point in the past the incoming terminal shrouds to one starter cubical had been removed for testing and not replaced. Along comes our electrician and shorts one of the incomers to earth with his screwdriver. Almighty flash and bang and the arc continued as the driver was still in the terminal. He returned and knocked the driver out of the terminal with a wooden chair. Only then did he go for first aid and then a very rapid trip to hospital!

Severe burns to his face and hands (his eyes were saved by his safety glasses) along with all the trauma that would go along with this.

Morning electrician arrives and is told of the accident along with being told to get the faulty drive going! What did he do, simple run 6mm singles out of the adjacent cubical door and in to the faulty cubical! OK He surrounded the area with bunting tape. Drive running management happy.

Enter Tony in the afternoon! Once I’d come out of orbit I was told to prepare plans to return the MCC to normal service the following weekend!

First off a survey of the panel (it was one I’d had little to do with before)

Supply either 1000A or 1200A ACB’s from the plant main board via 400mm singles to 1200A interlocked fuse switches (one on one off). Fed from the 1200A ACB.

Bus-bars 2” X ¼“ Al (under size)
Feeder drops to large drives 2 X 50mm Cu singles
Feeder drops to small drives 1 X 6mm Al singles (supper under size)

First idea, there were lots of spare cubicles so mount a 250A MCCB in one to feed all the small drives using 16mm double insulated singles to each drive. Management loved the idea and put it forward as safety suggestion of the month.

Enter “senior authorised person” “you can’t do that, it will set a president for all other panels”. We want safety but at no cost!
Safety suggestion of the month withdrawn.

Told to make the panel as safe as I could.

After being threatened with disciplinary action I was lumbered with the job. Rollicking No.1

  • Replaced all small drive feeder drops with 16mm double insulated singles
  • Remove all redundant feeder drops
  • replace all live terminal shrouds
  • Swap ACB’s to the lower 1000A feeder and adjust the O/L’s to 750A
Rollicking No.2 I didn’t inform accountancy of the change of feeders!
 
Last edited by a moderator:
As a follow on from the above I later found out the “senior authorised person” was involved in installing the panel :eek:
 
I was rereading this thread and spotted this;

“Didnt have the correct specific fuses on my person (who would?), so put standard 30 amp fuse wire into the fuse holders”.

If you look inside most plastic cartridge fuse holders you will see “Do not use wire fuses” the reasoning being if the fuse blows it creates ionised air. Ionised air is conductive so along with the atomised metal particles you effectively have a bomb. A wire fuse holder has a shaped arc path to dissipate heat, absorb the atomised metal and slow down the spread of ionised air.
 

Reply to 100amp 3 Phase isolater blew up in my face today... in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at...
    • Like
2 3
Replies
42
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top