Problem with a volt stick is if you put it near a spike light that you know has power on it you'd half expect at least that it would give you a live alarm even if the fitting casing was safe. The old neon screwdriver would give a more accurate result although even that wouldn't help if the outer casing only became live when it was moved.

Also as already mentioned there's a possibility that the 2 faults ie the CPC becoming disconnected and the now floating CPC wire coming into contact with supply voltage actually occurred in another fitting on the same circuit possibly some distance away so no amount of visual inspection would have helped either.

The only 2 ways I can see to mitigate the risk in this specific instance is either to isolate before touching or assume it's live and mitigate shock risk by having effective PPE like dielectric footware and gloves. Both of these measures would never be expected of the user of the installation so I guess it would be unreasonable to expect it of an electrician who's not doing anything that a everyday person wouldn't do.

We all know that we'd probably also have suffered the same outcome in this scenario because we'd probably have considered that the belt and braces approach of having a CPC along with the internal insulation resistance of wiring and components would protect us. The third thing that might have helped would be parallel earth paths providing sufficient current flow to cause the OCPD to disconnect but that obviously also didn't happen. The more I think about it the more it sounds like a scene from those movies where death goes looking for people who should have died in a plane crash but they managed to avoid it and they all start dying in very convoluted circumstances....
 
The problem with having insulated boots, gloves etc is that you could leave something that could kill someone else.

The only real way would have been to check that at least there was a working rcd.

I'm not knocking the O/P at all, as it's quite easily done.

A volt stick won't usually work when an L conductor is surrounded by metal, such as the metal light fitting.

Maybe the O/P will come back and let us know what the actual issue was.
 
These are pretty useful testers, I carry one in my kit and it's saved me a fair few times!
kewtech KT1700

Much more reliable than a voltstick.
I carry a couple of voltsticks, one fluke one which I rate more than the other one I carry kewtech duo. Bought this after being impressed by the KT1700.
The fluke voltage range is from 200v and not over sensitive.
The duo is from 90v and will tell you just about every wire is live!

The KT1700 has even found cut outs that have phenolic degradation that would have not been good if the seal fairy had been and I had gone to remove them!
 
Problem with a volt stick is if you put it near a spike light that you know has power on it you'd half expect at least that it would give you a live alarm even if the fitting casing was safe.
Possibly, but if I see that thing light up red, then I'm on my guard, and move it around a bit. If it still lights when close to a metal spike, then I'm not going to grab hold of that spike without checking further.
 
So, I'm still not 100% sure what caused the shock. I did find a CPC that had pretty much corroded out of the terminal block it was supposed to be in. Most of the JBs and lights had water ingress. I suspect a water-filled light created an L-E fault, but the disconnected CPC meant it was not tripping the breaker. Still, though, this doesn't explain why it tripped when it came to me being shocked. I ended up ripping most of it out, and yes, it is now on an RCBO until they upgrade the CU.

I would also suggest to everyone installing garden lights that whilst the flexible metal conduit looks the part, pretty much every run I found within this installation was full of water. If you're going to use a conduit use plastic slot conduit that allows water to drain out.

I've also decided to make some purchases off the back of this and I would suggest that anyone reading this takes note:

Kewtech KT1700 Single Pole Voltage Tester

From now on, I will use this on any metal fixing before I touch it.

ELECTRO SB FO E PL SR - Electrical safety trainer

Or


Yes, they're pretty ugly but if it stops me getting killed then it's worth it.



If anyone has any other recommendations, then fire away! We can all learn from this.
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
One of the things I can think of is to not use mains powered outside garden lights but to use the selv type.
 
VD only becomes a problem if the design of the circuit is poor and the size of the cables inadequate.

Well yes obviously, but if the transformer is indoors and your lights are 50m down the garden then it's very easy to need pretty big cables at 12V. It's fundamentally a bigger problem than when using 240V.
 

Reply to Today I experienced the worst electric shock my career in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top