I have to put 25 led down lights in a garage , customer wants them all on one switch line which will be 100 metres long. I'm going to use 1mm. Should I break them down into two lots of 14 ?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 100m switch line in the UK Electrical Forum area at ElectriciansForums.net
2.5mm don't be daft you wont get them in the terms
Another DIYer.28 down lights sorry
the startup current on LED lamps can be rather high !
id split the lamps on two circuits then wire them back to a single double pole contactor and then switch the contactor with the 100m switchline run.
once you've done your cable calc for the 100m run you will probably find a 1.5mm will be sufficient or a 2.5mm for luck ! lol