I have been to a job this morning, the outside carpark lights had a fault on them, i have rectified the fault. The system is TT with 100ma rcd incomer protecting the installation.

The problem is that if there is a fault on the lighting circuit throughout the night it takes the main 100ma rcd switch out shutting all power down.

If i put the outside lighting circuit on a 30ma rcbo would this over come the problem of tripping the main switch out if there is a fault and ONLY trip the 30ma rcbo for the outside lighting?
 
I found that you need to test each 100mA 'S' RCD with each 30mA RCD/RCBO combination to find out the precise time they disconnect. We know at 1 times they should operate between 130ms to 500ms and at 5 times they should operate between 40ms and 150ms but it is not always the case that discrimination is can be achieved.

The 4293 RCCBs have a lower front end of 200ms and maximum of between 300 and 400ms and often only trip near the maximum time allowed.
 

Reply to 100ma RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
295
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
277
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
368
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...