hello guys been called to a house today, Large old place with 3phase supply.
Phases into 100ma rcd then split to feed duel rcd wylex boards on each floor.The home owners have had trouble with the 100ma s type tripping but not any of the 30ma in the consumer units,i was thinking it may be a fault with a neighbouring property feeding back up the stake (TT system)

Any ideas on way forward,we need the 100 to protect the sub mains.

Cheers all
 
If this is a big property with scores of circuits, it could well be an accumulation of leakage current. Don't forget that it's very possible that none of the individual 30mA RCD devices are seeing 30mA, the 100mA will be seeing the overall leakage current. Then of course, there is always the probability of 100Ma S type device being faulty. The only way your going to really confirm or otherwise is to test with a leakage current clamp meter. Ramp testing will at best give you an idea, as they tend to ramp in multiples of test mA, sometimes in multiples of 5mA, depending on what range they are set on. You may well have to increase that front end device to a 300mA S type, ...only by careful testing will let you know that!!
 

Reply to 100ma stype tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
620
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top