hello all,

btw I'm a plumber.... do I hear groans?! I installed a new Neff oven, DB is 0.5m away through a wall, wired into spare 16A MCB (house was built 2019) with 2.5mm T&E via 20A switched outlet, manufacturers lead with moulded plug (wired into outlet - not shortened).

... plug lead into oven... pop... both RCD's trip.
... switch outlet on... ditto
... switch MCB on... ditto

Neff engineer came out, no difference... tripping RCD. Tested the oven with his test lead plugged into ring-main, absolutely fine, no issues. Conclusion: is the Neff lead is faulty, OK. (No replacement lead on vehicle!) replacement lead sent via courier turns up 4 days later.

... wired up new lead... pop... same issue.
OK, wired up original lead Neff into plug; plugged into extension lead, plugged into ring-main... oven fires up, no issues!

What am I doing wrong?? Is the 16A MCB faulty? Do I need to check continuity of 2.5mm T&E?

Please help...

Regards
Jim
 
Oh, would you believe it... moved neutral to other bar and NO ISSUE.....
How did you know that... :D? & why does (did) it trip...?
Thanks so much.
How do we know?

It happens countless times, and it’s always first thing we check.

As to why it trips…. Everything has an electrical load, in amps… as you may know.
An RCBO, or RCD basically measures what the load is on the live, and the neutral. If there’s a difference of 30mA, as standard, it will trip.

What you had was the life of the circuit going through one rcd, and the neutral going through the other…. So neither was balanced…. Rcd trips.
 
Neff engineer came out, no difference... tripping RCD. Tested the oven with his test lead plugged into ring-main, absolutely fine, no issues. Conclusion: is the Neff lead is faulty, OK. (No replacement lead on vehicle!) replacement lead sent via courier turns up 4 days later.
And Neff had the cheek to call him an engineer, perhaps he was a mechanic.
 
That’s not fair on the Neff engineer.

He only knows his specific product, and probably has to follow a troubleshooting guide that Neff themselves has written.

They just assume as mains socket outlet works… as it would with a plug in tester.


It would be like asking a dentist to have a look at your feet. 😂😊
 

Reply to DIY - new oven tripping DB. in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
433
Oh I see. I will check that one as well. Thank you!
Replies
5
Views
299

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top