G
greenspark
I was testing the above RCD yesterday on my Megger MFT1553 using the Autotest function set to the correct trip range of 100mA but I couldn't get a response from the RCD even at x1. At this point, the meter would simply flash <50V. I then retried the test using the manual functions but still got the same result. I know that the Earth Fault Path was terrible but I tested a 30mA RCD on the same installation and got it to operate successfully through all trip currents.
What I am concerned with is whether:
1.
It was the meter or the person operating it causing this problem,
I.E: I held down the blue 'degree' button to try to change the RCD Type to S (Time Delay) but it didn't seem to give me a clear S option.
OR,
2.
A 100mA Type S RCD actually needs a better earth fault path to operate within time than a 30mA RCD or possibly just in this case due to this particular 100mA RCD. I suppose to find out the latter I would need to try replacing the RCD for like with another.
Interested to know your thoughts on this, I know I've gone to town on this message but knowledge is power. An apt description for our trade I reckon.
What I am concerned with is whether:
1.
It was the meter or the person operating it causing this problem,
I.E: I held down the blue 'degree' button to try to change the RCD Type to S (Time Delay) but it didn't seem to give me a clear S option.
OR,
2.
A 100mA Type S RCD actually needs a better earth fault path to operate within time than a 30mA RCD or possibly just in this case due to this particular 100mA RCD. I suppose to find out the latter I would need to try replacing the RCD for like with another.
Interested to know your thoughts on this, I know I've gone to town on this message but knowledge is power. An apt description for our trade I reckon.