Hi
I'm about to quote on a 10KWp system, which will be one of the first of my own as i am newly MCS accredited. I'm getting to grips with most of this but i have a couple of questions
If i split it over the 3 phases can i do this install (all 3) as G83? If so then i guess i can do 3x 4KWp. So what FIT bracket does this fall in? <4KW or 4-10KW?


Thanks all
 
G83 allows up to 16A a phase. As far as the rules go, you shouldn't even need to contact the DNO till you've installed it. Having said that, it's never a bad idea to speak to the DNO.
 
Ok, as i thought, only need to contact DNO before installation if G59. So i can split over 3 phases and install as per G89. So is it actually 3680W (16A) max per phase or 4KW? This seems a bit of a grey area, or am i wrong?
 
Although DNOs have different ways of dealing with things, most will allow more than 3.68kW under G83.

EDF used to but now they are UK Power Networks the last time I spoke to them (Forget it's the same guy as when it was EDF!!) they will not let it go higher. Think a few installers in the UKPN area may be court out. I have to speak to them again in a few weeks time so it may well of changed again!
 
EDF used to but now they are UK Power Networks the last time I spoke to them (Forget it's the same guy as when it was EDF!!) they will not let it go higher. Think a few installers in the UKPN area may be court out. I have to speak to them again in a few weeks time so it may well of changed again!

What have they suggested for >3.68kW systems?
 
That's crazy! They have effectively priced any >3.68kW system out of the market.

Yep! I have heard they asked for ÂŁ120 for a survey and agreed to the installation there and then! So I think it's a money making scam at the moment. Why pay a penny for a visual survey to say yes OK?

As I say things may well change again. For UKPN it's early days.
 
As long as the ÂŁ120 survey is all they ask for then all should be good. If the relays and testing are insisted on then the costs will be ridiculous.
 

Reply to 10KWp system over the phases in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
633

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top